We're already there at 480v Kwired. The transformer idea had crossed my mind however. It's alright though, we have a Plan B.
Step up voltage so you can use smaller conductors
Unless you are already at 480 volts, then you get into needing over 600 volt conductors and equipment.
Interesting discussion, this was the wire I was referring too:
http://www.servicewire.com/serviceplex-v2.php
FWIW. I am fairly sure the grounding conductor is not a part of the cable unless it is the same size as the other conductors. If a smaller ground is pulled with this cable off of a separate spool is it now subject to a 31% fill? If it were sheathed?It would of been spun into the cable.
I realize that, question is would it reduce needed conductor size enough to fit the raceway. I guess it is about a 20% change of voltage, maybe it would be enough.There do exist AC voltage systems at 600V phase to phase. They are rare in the USA, but they do exist.
A cable is a cable with or without a sheath. IMO
You leave my grandmother out of this.I found a home and garden forum where a little old lady diyer says a multlconductor assembly has to have an overall outer covering to be considered one cable.
I don't suppose you will take that as an authoritive source?
I am guessing prolly not.
You leave my grandmother out of this.
My grandmother can kick your grandmother's behind