vasectomy7
New User
- Houston, TX
- Maintenance electrician
[I'm just an apprentice so I apologize in advance if I sound like an idiot]
I work as an in-house electrician at an industrial facility; I have been told several times by the senior electrician that whenever a lockout-tagout is done, we are required to use the M.C.C. bucket for that purpose. He says it is never acceptable to just lockout at the "local disconnect," right at the particular motor / machine. Is that an official rule in the NEC or 70e?
The most I can find is
Scenario: The drive chain on a screw conveyor has come loose, it needs to be inspected and retightened. Before starting work, which disconnect should be locked?
This is the circuit:
GRID POWER ----> Main 4160v transformer with disconnect ------> 480v M.C.C. bucket with disconnect -----> PLC contactor with manually tripable overload -----> Local disconnect, 10' from the motor -----> Motor
NFPA 70e Article 120.4 (B) (11) (1) "Lockout shall be defined as installing a lockout device on all sources of hazardous energy such that operating of the disconnecting means is prohibited. The tagout device shall be installed in the same position available for the lockout device"