I have to hook up 5) 230v 1/2hp sf. 1 and code letter K with internal overloads.. These motors are all the same, they are fans and continuously used.
I was checking to see if I can put three of these motors on one branch circuit.
Per T430.248 my full load current is 4.9
4.9x1.25 continous=6.125
+4.9 2nd motor
+4.9 3rd motor
15.92 Amps on a #12 awg wire
4.9x250% inverse time breaker = 12.25
+ 4.9
+ 4.9
=22.05 so I would round down to 20 A and if it doesn't hold put it on a 25A Breaker