We are conducting MV cable testing. Length of cable is 7.2 Km. It has 14 joints. It was laid down almost one year back and was not put into service due to some reasons. It was lying on ground.
Now when we wanted to put this cable in service, we started its testing. For insulation, we tested it at 5 KV for one minute, but we do not get stable value, it is all the time fluctuating between 200 G ohms to 800 G ohms. Fluctuation is not understood.
What may be the reason for fluctuation? What remedial measures can be taken? Can we go ahead for Dc withstand test or AC test? And if the cable clears these tests can we put this cable in service.