I have seen that but it was during the late 60's, not sure why??????
Hehehehehe:grin::wink::grin:
I have seen that but it was during the late 60's, not sure why??????
It's all good :smile: ........ well no the CMPs comments are not good, I swear they whipped that one out with little to no thought at all.
In my first post when I said I was lost I was talking about the CMP comment, it makes no sense at all.
I argee - as mentioned it is a contradiction. Since there was at least a dozen or so proposals seeking to clarify the issue in one way or another - they sought to avoid this issue and further the contradictions in the code with their comments. (And no, I'm not upset that they did not accept mine - but responded to Mike Holts in this case with aforementioned fence sitting comment.)It's all good :smile: ........ well no the CMPs comments are not good, I swear they whipped that one out with little to no thought at all.
In my first post when I said I was lost I was talking about the CMP comment, it makes no sense at all.
5-157 Log #3051 NEC-P05Final Action: Reject
(250.52(A)(3))
_______________________________________________________________Submitter:Mike Holt, Leesburg, FL
Recommendation:Revise text as follows:
(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.)
of concrete, located horizontally near the bottom or vertically, and within that
portion of a concrete foundation or footing that is in direct contact with the
earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized
or other electrically conductive coated steel reinforcing bars or rods of not less
than 13 mm (? in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare
copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted
to be bonded together by the usual steel tie wires or other effective means.
Exposed or concealed reinforcing bars that are bonded to reinforcing bars
meeting the criteria of this section shall be considered part of the electrode.
Where multiple concrete-encased electrodes are present at a building or
structure, it shall be permissible to bond only one into the grounding electrode
system.
Substantiation:There is a long standing debate as to whether or not a piece of
rebar (connected to the footing/foundation steel) that pierces the concrete and is
installed inside of a framed wall can be connected to and be used as a concrete
encased electrode. This proposal is intended to clarify this practice is a
permitted one.
Panel Meeting Action: Reject
Panel Statement:Only the portion of an electrode that is in contact with the
earth can be called an electrode. The exposed portion of the rebar could be
used as a connection point but cannot be considered as the electrode.
Number Eligible to Vote: 16Ballot Results: Affirmative: 16
Hey, Bob -
I think we'd both say they're wrong.![]()
For the sake of argument I will say the sky is green and the grass is blue. :grin:
I'm sure.I have seen that but it was during the late 60's, not sure why??????
How do you know the entire 20' is still there when the concrete is poured?To me one of the great things about a CCC is that it could be 'permanent' if say a 4 AWG is run directly from the panel and all the way into the footing pour, the copper will not give out before the building does.
You don't - and frankly, who cares?!? That 20' is connected to another 20', and none of it is directly connected to the earth. While both concrete and steel are both conductors, the concrete is in connection with the earth, and only the steel counts???? Only part of it?!?How do you know the entire 20' is still there when the concrete is poured?
How do you know the entire 20' is still there when the concrete is poured?
Is the five feet of metal water pipe on the inside of a building electrode?
Yes, explain how
No, explain why not
It is because the code tells us it is.:grin:Is the five feet of metal water pipe on the inside of a building electrode?
Yes, explain how
No, explain why not
So would be the 24" of 10' ground rod you can leave above ground.
Where does it say that the five feet is part of the electrode?![]()
Like we were discussing last year....
If it is okay to connect to rebar which extends out of the slab, what is to stop me from running rebar above grade all the way to the service and bonding it to the service enclosure? Maybe with a little bitty short 4" piece of copper wire as the GEC?
Like we were discussing last year....
If it is okay to connect to rebar which extends out of the slab, what is to stop me from running rebar above grade all the way to the service and bonding it to the service enclosure? Maybe with a little bitty short 4" piece of copper wire as the GEC?
the two feet of a 10 foot rod sticking out of the ground and including the rebar that is turned up out to the footing is nothing more that what is described in 250.64(F)(3) and is not the electrode itself. The electrode must be in contact with earth no matter how useless it might be. [/SIZE][/FONT]
As long as there is 20 feet of rebar in contact with earth through the footer what would be wrong with this installation?
Can one not do the same thing with building steel?