dnem said:
"In my neck of the woods" its common not to have the basement floor poured at the time of the roughs [pumbing, HVAC, elect]. . Sometimes the basement is still a mud pit, other times it's stoned and mostly ready for the pour but still not poured.

Would you attempt the stilts if it's not poured ?

I would do it as long as it's not muddy. Mud and stilts just don't mix, but if it was dry the dirt doesn't bother me much.
 
augie47 said:
looks like an open invitation to violate NEC 310.15(B)(2)

At the linked site

http://www.speedwayelectricalproducts.com/

click on the Product Info red button

take that page down to the bottom and you'll see a blue outline box that says:

Maximum Number of Installed Cables Allowed

Because Speedway is classifies as an open topped Cable Tray, for ampacity you get bounced to 392.11(A)(1) which doesn't require you to derate.
 
dnem said:
At the linked site

http://www.speedwayelectricalproducts.com/

click on the Product Info red button

take that page down to the bottom and you'll see a blue outline box that says:

Maximum Number of Installed Cables Allowed

Because Speedway is classifies as an open topped Cable Tray, for ampacity you get bounced to 392.11(A)(1) which doesn't require you to derate.

I would have to study to confirm my thoughts. But, initially, I'm still having difficut time buying into that. Since Romex is not "TC" rated, I'm not prone to treat it as a tray cable conductor.
Sounds like smooth sales talk to me (so far)
 
it does say its UL listed and says it passed the tempature test. i think its a really good product. didnt arlington have a product similar to this or is this the same thing?
 
electricalperson said:
it does say its UL listed and says it passed the tempature test. i think its a really good product. didnt arlington have a product similar to this or is this the same thing?

Hmmm..... just because somthing is listed to accept NM, does it mean that NM is legal to be used in it? does UL and NEC go hand in hand on this kind of stuff?
 
electricalperson said:
it does say its UL listed and says it passed the tempature test. i think its a really good product. didnt arlington have a product similar to this or is this the same thing?

You are correct, Arlington makes a product very similar to this. They call it "cableway"
 
ultramegabob said:
Hmmm..... just because somthing is listed to accept NM, does it mean that NM is legal to be used in it? does UL and NEC go hand in hand on this kind of stuff?
where in the code book does it say its illegal to use that raceway for NM? wont 110.3B cover that?
 
augie47 said:
I would have to study to confirm my thoughts. But, initially, I'm still having difficut time buying into that. Since Romex is not "TC" rated, I'm not prone to treat it as a tray cable conductor.
Sounds like smooth sales talk to me (so far)

I agree. I am pretty sure if I built an open top "wireway" like this out of plywood and put 38 runs of 14-2 in it that I would(and should) get red tagged. What is the difference besides a "listing" either way I am piling a bunch of NM cables on top of each other.
 
would it be safe to assume this system falls under 392 cable trays? NM cable can be installed in a cable tray. by the definition of cable tray, cable tray is designed to support raceways and cables.
 
I am really interested in hearing what more learned folks than I have to say on this. After some study, I realize my concern about TC is not valid.
NM cables are acceptable in Cable Tray. 392.11 (A)(1) seems to say that as long as each cable does not exceed 3 cc conductors then derating doesnt apply.
I am having a difficult time seeing how 310.15 states "bundling" of cables requires derating, but 392..11(A) ststes that in the case of 12/2 or 12/3 NM in "cable tray" derating doesnt apply when they could be the same as bundled..
 
dnem said:
If you use Speedway [plastic gutter] across the basement, you can't beat running thru the basement.

You can if you are in the land of 'strapping'.;) :grin: (or furring for those not familiar with this term.)
 
fireryan said:
I thought you couldnt run exposed romex in a basement and by the looks of the picture they are doing just that

You can run exposed Romex as long as you follow the rules [334.10(A)(1)]. . You can't run it exposed when required to be behind 15min rated finish as in most types of commercial buildings [334.10(3)]. . You can't run it above a nondwelling drop ceiling [334.12(A)(2)]. . You can't run it in an air handling space with nonducted cold air returns [300.22(C)(1)].

You can run it exposed other times when you follow 334.15.
 
fireryan said:
I thought you couldnt run exposed romex in a basement and by the looks of the picture they are doing just that

"by the looks of the picture"
Are you talking about the picture on the Speedway website ?
That site shows a basement ceiling which fails under 334.15(C). . The (C) section is even less restrictive than the rest of 334.15. . You can run exposed and you can run midair thruout the joists and even tack the larger Romexs to the bottom of the joists, if you wish.

Once you get out of the ceiling, you still can run exposed. . But you pick up additional code language of "closely follow the building finish or of running boards" [334.15(A)]. . The inspector might also make the interpretation that you need "protected from physical damage where necessary" and require conduit on the wall [334.15(B)]. . He might have certain criteria where only certain wall situations/exposures require conduit. . Outside requires a minimum conduit cover for the first/bottom 8 feet [300.5(D)(1)]. . Inside is open to the interpretation of "where necessary" [334.15(B)]. . In our jurisdiction, we never require basement conduit over wall mounted Romex until you start running it lower than about 4 feet from the floor.
 
fireryan said:
Our inspector doesnt allow it here anyways

Is he "shooting from the hip" ? , the "not in my town" personality or does he actually have authority under law to modify the NEC ?
 
fireryan said:
What does this mean?

"Strapping" means 1x3 boards nailed 16" o.c. perpendicular to the joist to which the drywall or blueboard is fastened to. This creates a void where you can install the romex under the joists. So running romex this way is faster imo than through a basement. But you use about 10' more cable per home run than if you dropped to the basement. Unless you pull hr's diagonally as the crow flies.
 
j_erickson said:
fireryan said:
j_erickson said:
You can if you are in the land of 'strapping'.;) :grin: (or furring for those not familiar with this term.)
What does this mean?
"Strapping" means 1x3 boards nailed 16" o.c. perpendicular to the joist to which the drywall or blueboard is fastened to.
Here's an example of an older strapped ceiling:

DSC01164.JPG
 