N-G bond

I’m losing interest in doing this. Bus bar cannot be removed from the N-G bond. If this means that it creates a second N-G bond at the subpanel breaker powering the bus, then it will not be possible. Doesn’t really make sense though.
 
Also, to be clear, the only thing powering the bus bar will be a 200A loads breaker that does not itself have a N-G bond. But the N and G will need to be placed on the bars in the main panel that are bonded, creating N-G bond for this breaker. Is this a problem?
 
Don’t think N is insulated in the meter socket. Our utility approved the use of meter socket for this purpose.
Yes, but you will have an illegal second bond, unless you convince the inspector that the first breaker is the emergency disconnect. Doesn’t matter what the utility company approves after their meter, they have no jurisdiction.
 