Is the neutral insulated in the meter socket? Most are not.There is no meter in the customer meter socket. It has a Tesla Backup Switch meter collar and a jumper cover.
Yes, but you will have an illegal second bond, unless you convince the inspector that the first breaker is the emergency disconnect. Doesn’t matter what the utility company approves after their meter, they have no jurisdiction.Don’t think N is insulated in the meter socket. Our utility approved the use of meter socket for this purpose.
Is the utility meter in with the main panel? Meaning, is this a meter-main panel?I will definitely check this. Thank you for your good guidance.