Nail plate the back of a plastic box ???? Really???

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
A local combo inspector recently turned down an inspection on 2 new houses because, the deep Carlon plastic boxes are too close to the surface of the wall on the backside. He wants them all nail plated. My interpritation of the code on this is, when the NM is running through the stud it needs to be plated, but when it is on the side of the stud there is no need to nail plate it. I thought Carlon had addresssed this issue before, does anyone have info on that? This has delayed the completion of the houses for no good reason, I have yet to see any job where this has been required. Any helpful comments would be welcome.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Cables on side of studs need to be kept 1-1/4" from edge of stud or otherwise be protected from penetration by nails, screws, etc.

That said, he is asking you to protect a box and not a cable.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Cables on side of studs need to be kept 1-1/4" from edge of stud or otherwise be protected from penetration by nails, screws, etc.

That said, he is asking you to protect a box and not a cable.

This is where it gets "questionable" where the NM goes into the box (factory KO's) it is closer than 1 1/4". I have yet to see ONE job in 34 years where this was required, my oppinion is it is personal and I see no place for that in his job.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
What does he think will be nailed into the box? A picture? I guess the inspector has never seen a screw ran through the breaker panel from the meterbase.
That being said, is he also requiring you to install nail plates to the backside of the breaker panel, or is it surface mounted...I know, it is metal.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
This is where it gets "questionable" where the NM goes into the box (factory KO's) it is closer than 1 1/4". I have yet to see ONE job in 34 years where this was required, my oppinion is it is personal and I see no place for that in his job.


I understand that also, have never been giged for it, is also a little hard to win either side of that argument. The main idea of keeping cables 1-1/4 from edges of studs is so nails or screws securing the wall finish will not damage cable if they miss the stud. I do try to keep cables as far away as practical when entering these boxes, and can not recall ever having to fix a damaged cable in this area in about 25 years, so I would say the chance of damage is pretty slim.

What does he think will be nailed into the box? A picture? I guess the inspector has never seen a screw ran through the breaker panel from the meterbase.
That being said, is he also requiring you to install nail plates to the backside of the breaker panel, or is it surface mounted...I know, it is metal.

The biggest problem is the back side of wall from where the outlet box opening is. I have occasionally seen nails or screws penetrate a box, as well as a panelboard. The guy installing the meter on back side should know better, especially after doing it once before. I have run into that problem more often when other items are mounted back side of where panel is. Seen screws for hanging shelves, cabinets, etc on back side of wall penetrate anything you can imagine inside wall, even seen kitchen cabinets supported by plumbing in wall instead of studs.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
This is where it gets "questionable" where the NM goes into the box (factory KO's) it is closer than 1 1/4". I have yet to see ONE job in 34 years where this was required, my oppinion is it is personal and I see no place for that in his job.

I thought that at first, then I read 300.4(D) It doesn't say cables attached to studs, it says cables run parrallel to... So I am of the opinion that if the inspector can put a tape measure on the edge of the stud and measure less than 1 1/4" (as the crow flies) to the romex, or even MC, then he is properly executing the exact wording of the NEC. Whether others have picked this up in the past or not.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
I thought that at first, then I read 300.4(D) It doesn't say cables attached to studs, it says cables run parrallel to... So I am of the opinion that if the inspector can put a tape measure on the edge of the stud and measure less than 1 1/4" (as the crow flies) to the romex, or even MC, then he is properly executing the exact wording of the NEC. Whether others have picked this up in the past or not.

That could possibly mean don't use the cable opening in the box that is right next to the stud. I kind of have no problem with that logic, but like I said before - never been asked to change these, and can not recall ever having an incident where cable was damaged in over 25 years, so I think the risk is very small if you do use that cable opening.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Dangerous damage should be picked up by an ARC fault .Yes!
The drywaller should know there is a box near the stud.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Cables on side of studs need to be kept 1-1/4" from edge of stud or otherwise be protected from penetration by nails, screws, etc.

That said, he is asking you to protect a box and not a cable.

IMO the inspector is thinking the same thing. Bogus but enforceable by the wording of the NEC unless you enter the box KO at least 1.25" away from the stud.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Dangerous damage should be picked up by an ARC fault .Yes!
The drywaller should know there is a box near the stud.

The problem is on the back side not the side with the box opening. When they are driving nails/screws next to the cut out they know exactly where the box is. When they are hanging opposite side of wall there is no cut out and they have no idea the box is there if they miss the stud with nail/screw, and the cable also enters the box closer to that side of the wall.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
A local combo inspector recently turned down an inspection on 2 new houses because, the deep Carlon plastic boxes are too close to the surface of the wall on the backside. He wants them all nail plated. My interpritation of the code on this is, when the NM is running through the stud it needs to be plated, but when it is on the side of the stud there is no need to nail plate it. I thought Carlon had addresssed this issue before, does anyone have info on that? This has delayed the completion of the houses for no good reason, I have yet to see any job where this has been required. Any helpful comments would be welcome.

He is correct and you must also install one of these over the front of the box.

nail plate.jpg

IMO the inspector is thinking the same thing. Bogus but enforceable by the wording of the NEC unless you enter the box KO at least 1.25" away from the stud.

Both bogus and NOT in the NEC. You would never be able to enter a outlet.


Ask him how a nail or screw can enter the face of a stud then enter the back of a box. Does he still believe in the magic bullet? (Kennedy for you younins)

(D) Cables and Raceways Parallel to Framing Members
and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (11⁄4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate
. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm (1⁄16 in.) thick.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
He is correct and you must also install one of these over the front of the box.

View attachment 7253



Both bogus and NOT in the NEC. You would never be able to enter a outlet.


Ask him how a nail or screw can enter the face of a stud then enter the back of a box. Does he still believe in the magic bullet? (Kennedy for you younins)

(D) Cables and Raceways Parallel to Framing Members
and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (11⁄4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate
. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm (1⁄16 in.) thick.

You're reading that section incorrectly. If the cable is secured at least 1.25" from the face of the stud and enters the box in a KO at least 1.25" from the stud then it's code complaint.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
You're reading that section incorrectly. If the cable is secured at least 1.25" from the face of the stud and enters the box in a KO at least 1.25" from the stud then it's code complaint.

Disagree. If it is 1/8th of an inch away from the stud it is no longer parallel to the stud.

So tell me how to use this box?

pfbox.jpg
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Disagree. If it is 1/8th of an inch away from the stud it is no longer parallel to the stud.

So tell me how to use this box?

View attachment 7254
That box the cable enters the back wall which is your protection from screws or nails that are securing drywall or other wall finishing material.

Parallel to stud? Is'nt the next stud 14-1/2 inches away also parallel to the stud in question? If so why is a cable 1/8 inch away not parallel? It is certainly much closer to parallel than it is to perpendicular.:happyyes:
 

TobyD

Senior Member
Ive been through the same issues before.I have also had siding nails shot through into the bus bar on a few load centers too.We normally make up the breaker panel on the rough.But, as of late we wait until the final .We remove the interior from the box too.I have seen closet shelf hanger scews driven into the breaker box too.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
That box the cable enters the back wall which is your protection from screws or nails that are securing drywall or other wall finishing material.

Parallel to stud? Is'nt the next stud 14-1/2 inches away also parallel to the stud in question? If so why is a cable 1/8 inch away not parallel? It is certainly much closer to parallel than it is to perpendicular.:happyyes:

It enters the box within 1 1/4" of the edge of the stud or joist.

It says "installed" parallel. That means where it is attached.

Ive been through the same issues before.I have also had siding nails shot through into the bus bar on a few load centers too.We normally make up the breaker panel on the rough.But, as of late we wait until the final .We remove the interior from the box too.I have seen closet shelf hanger scews driven into the breaker box too.

Not my job to protect from stupid. Yes the nails went through the wires.

nails.jpg
 