ParagonBuilder
Member
- Location
- Norwich, CT
Is there a code that states that we must follow nameplate data. I wired a 2-1/2 ton furnace yesterday, and my boss wanted to know why I didn't run 12 gauge. He says, "We always run 20 amp circuits for dedicated runs, and besides motors require a min of 20 circuits per NEC."
I showed him the nameplate which was 11 amp minimum ampacity and 15 amp maximum over current device.
He said manufacturers cannot overrule the NEC.
He is supposed to show me this 20amp motor rule...
I find nothing other than the standard 125 percent calcs.
As far as I understand it, if he wants to run 20 amps to the furnace it would need an ssu or equivalent.
Am I off base here?
I showed him the nameplate which was 11 amp minimum ampacity and 15 amp maximum over current device.
He said manufacturers cannot overrule the NEC.
He is supposed to show me this 20amp motor rule...
I find nothing other than the standard 125 percent calcs.
As far as I understand it, if he wants to run 20 amps to the furnace it would need an ssu or equivalent.
Am I off base here?