NEC 110.14 and highly stranded wire on oven

That's not what 110.14 says. It says that for other than Class B and Class C, the connector "shall be identified for the specific conductor class or
classes."
I agree with Larry
To me, this is a non-issue, and I wouldn't bother asking anyone.

I would use regular wire-nuts and simply make good connections.
this only a NEC wording issue.
Its not practical to UL list every type of stranded wire a wirenut can be combined with, and it does appear to be a common practice, many lighting fixtures now only come come with metric wire of a unknown stranding.
my fix would be add an exception
something like
Proposed Exception to 110.14(C):
Exception: Splicing wire connectors, including twist-on and lever-type splicing connectors, identified for use with stranded copper conductors not larger than 10 AWG shall be permitted to splice copper conductors more finely stranded than Class B and Class C, provided the conductors are within the connector’s marked conductor size range.
 
I agree with Larry this is not a practical issue, but a NEC wording issue.
Its not practical to UL list every type of stranded wire a wirenut can be combined with, and it does appear to be a common practice, many lighting fixtures now only come come with metric wire of a unknown stranding.
my fix would be add an exception
something like
Proposed Exception to 110.14(C):
Many lighting fixtures include the wire nuts. I would expect that those wire nuts would be suitable since they’re included with the listed fixture.
 
Many lighting fixtures include the wire nuts. I would expect that those wire nuts would be suitable since they’re included with the listed fixture.
I have looked into this before and am going to agree with Don here, I am not aware of any wire nut that has been identified for use with finely stranded conductors, even ones that are supplied by manufacturers with a light fixture.
Look at the last part of the parent text of 110.14.

I am not aware of any wire nut that has been identified for use with finely stranded conductors.
 
I have looked into this before and am going to agree with Don here, I am not aware of any wire nut that has been identified for use with finely stranded conductors, even ones that are supplied by manufacturers with a light fixture.
I don’t disagree with that. But supplying wire nuts that are not suitable for use included with a listed fixture shouldn’t happen.
 
Wall ovens and cooktops always come with whips, never terminal blocks.

Wire-nuts may not be listed for the connection but they have been the standard connectors used for 60+ years. I have never run across a problem unless the wrong size connector was used or wires were not stripped long enough.
Kinda like the thread about protecting NM cable where it enters the plastic box and is too close to the face of the stud.

Been doing it for 40+ years with little known adverse consequences.

Maybe the wire nut and finely stranded wire is just another example.
 
Kinda like the thread about protecting NM cable where it enters the plastic box and is too close to the face of the stud.

Been doing it for 40+ years with little known adverse consequences.

Maybe the wire nut and finely stranded wire is just another example.
ist only been in the NEC since 2011, the proposals that created this limitation stemmed from issues unique to solar photovoltaic systems and other types of splicing wire connectors, not standard wirenuts splicing a 14 AWG solid to a 18AWG Class K stranding fixture wire.
 
Interesting thread yet no one has provided any proof that these oven use conductors with more than 19 strands. :unsure:
 
Never been a big fan of wire nuts for #8 or #6. Polaris are much nicer and make for a more tidy box. Split bolts are fine too, less expensive, but a little more work than a Polaris.
 