What are your thoughts on this:
The code mandates working space for electrical equipment “likely to require examination, adjustment, servicing, or maintenance while energized.”
A non-fused disconnect for an AC unit is between the AC and the main panel and its purpose is to isolate the condenser for service. There is no need to examine, service, adjust or maintain a non-fused disconnect while it is energized. Want to check the voltage you say? Well do that at the breaker in the main panel or at the AC unit, then determine if you need to pop open the on/off switch (the non-fused disconnect)
There are homes with non-fused disconnects, from the 80s that are still in use. It is not likely that one of these will be “likely to require examination, adjustment, servicing, or maintenance while energized.” under normal conditions. There is no OCPD, no exposed energized parts with the cover on, nothing to adjust while energized, Schneider Electric’s safety guidelines, aligned with NFPA 70E, recommend that maintenance tasks—such as inspecting terminals or tightening connections be performed only when de-energized, following lockout/tagout procedures.
Thoughts ?
The code mandates working space for electrical equipment “likely to require examination, adjustment, servicing, or maintenance while energized.”
A non-fused disconnect for an AC unit is between the AC and the main panel and its purpose is to isolate the condenser for service. There is no need to examine, service, adjust or maintain a non-fused disconnect while it is energized. Want to check the voltage you say? Well do that at the breaker in the main panel or at the AC unit, then determine if you need to pop open the on/off switch (the non-fused disconnect)
There are homes with non-fused disconnects, from the 80s that are still in use. It is not likely that one of these will be “likely to require examination, adjustment, servicing, or maintenance while energized.” under normal conditions. There is no OCPD, no exposed energized parts with the cover on, nothing to adjust while energized, Schneider Electric’s safety guidelines, aligned with NFPA 70E, recommend that maintenance tasks—such as inspecting terminals or tightening connections be performed only when de-energized, following lockout/tagout procedures.
Thoughts ?