NEC ? 2008 Code

Status
Not open for further replies.

ahartma

Member
Location
Afghanistan
What is the correction factor for Type ZW conductors installed in conduit exsposed to direct sunlight 51 MM above a rooftop and at an ambiant temp of 39 degrees C ?
 
What is the correction factor for Type ZW conductors installed in conduit exsposed to direct sunlight 51 MM above a rooftop and at an ambiant temp of 39 degrees C ?

See Table 310.15(B)(2)(c). At 51 MM the correction factor is 22?C.

22C+39C=61?C

See Table 310.16. The correction factor is .33 for type ZW.
 