Do you know if the main breaker in an exterior MDP will qualify? Austin Energy (where I am) has required an external disconnect for years and the MB in the MDP if it's externally mounted satisfies them.there is a new requirement in 230.85 that applies to one and two family dwellings that requires a disconnect for emergency purposes to be installed at a readily accessible outdoor location. It can also be the service disconnecting means or it can be just a switch that is not the service disconnecting means. Needs to be marked accordingly and there is no mention of location relative to metering, just that there needs to be an outside disconnect for emergency purposes.
I don't see why not. New code section does tell you how you must label it, so you will need to add "EMERGENCY DISCONNECT" to your usual SERVICE DISCONNECT labeling.Do you know if the main breaker in an exterior MDP will qualify? Austin Energy (where I am) has required an external disconnect for years and the MB in the MDP if it's externally mounted satisfies them.
I can see a new Halloween prank-- see how many breakers you can shut off before the cops show up!
The thing that code leaves somewhat vague however is that if said disconnect meets criteria for a "service disconnecting means" then must one consider it to be the service disconnect and run your GES to that point as well as keep grounded and grounding conductors separated beyond that point? It is reasonably clear that an unfused switch is permitted to be used as this emergency disconnect but does not make it clear if you can use something that otherwise qualifies as a service disconnect yet place the service disconnect somewhere down stream from it.We see many of Our commercial customers that have this already.
meterbase combo panels like a MH uses should qualify the way I read it as long as its marked.
of course, it will probably be four or five years before we are on it...
I can see a new Halloween prank-- see how many breakers you can shut off before the cops show up!
I have a padlock on mine.Many houses around here have outside panels and I've never heard of a vandal turning off someone's breakers.
That will just slow down your waiting timeI have to say, every time I drive through a Mcdonalds drive thru I think about jumping out and pulling that big handle down.
JAP>
That will just slow down your waiting time
Might as well plan on leaving after you pull that handle, your wait went from long to eternity.The long wait is what triggers the want to jump out and pull the handle in the first place.
JAP>
Might as well plan on leaving after you pull that handle, your wait went from long to eternity.
Add: power going out is bad enough, the fact the computers went down potentially killed business for the rest of the day.
Then you have to work your way backward in the line, that disconnect is usually back near the ordering station and not by the receiving station.Pull the handle AFTER you receive your order. Problem solved.
Clear as mud, huh.The thing that code leaves somewhat vague however is that if said disconnect meets criteria for a "service disconnecting means" then must one consider it to be the service disconnect and run your GES to that point as well as keep grounded and grounding conductors separated beyond that point?
Not sure what 250.25 is all about just yet. 250.24 (A)(1) I think is unchanged and has always let you land the GEC at any point between service drop/lateral and the service disconnecting means, which commonly allowed us to land it in a meter socket (where POCO will allow it). Emergency disconnect that is not the service disconnecting means would still be allowed to be a place where you can run the GEC as it is between the service drop/lateral and the service disconnecting means.Clear as mud, huh.
2020 NEC 230.85 option 3 appears to allow equipment that meets the criteria of a "service disconnecting means" and label it NOT SERVICE EQUIPMENT and now it is not what it is and you can run 3-wires inside to a main breaker panel without separating the neutrals and grounds.
An option 3 disconnect meeting the criteria for a "service disconnecting means" must also comply with new 2020 section 250.25 and have a 250.24(B) Main Bonding Jumper and a 250.24(D) Grounding Electrode Conductor connected to grounding electrode(s) required by Part III of article 250.
Any clearer now? Not to me as now both inside and outside pieces of equipment will need to be connected to a GES.
Other interpretations needed.