That doesn't work.
First, if it's 'NOT SERVICE EQUIPMENT' then it shouldn't have the neutral-ground bond that comes standard on meter mains, which are often labeled 'suitable for use only as service equipment'. So you can't go taking something labeled as such by the manufacturer and stick a label on it that says 'NOT SERVICE EQUIPMENT.' That's either the wrong equipment or the wrong label.
Bingo. That's the big issue here in Massachusetts. The Code Gurus here are saying that a standard 200-amp meter-main CAN be used as the ED for option #3 in 230.85...Just put the label on it NOT SERVICE EQUIPMENT, pop a 3-wire SEU inside to a Main Breaker panel which will be your so called Service Disconnect.
Sound familiar jaggedben ... same as the PV Disconnect label on a piece of service equipment. Throw a label on it and it aint what it is anymore.
Good point though on the... 'suitable for use only as service equipment'...I will look for that labeling. SUOSE vs SUSE