shortcircuit2
Senior Member
- Location
- South of Bawstin
In reading the 2020 Code, if an installer selects 230.85(3) for the Emergency Disconnect, 250.25 directs the installation to comply with 250.24(A)-(D)...which will require a GEC connected to the GES
The 230.85(3) Emergency Disconnect labeled NOT SERVICE EQUIPMENT now requires a Service Disconnect after either outside or inside nearest the point of entrance...which also requires a GEC connected to the GES according to article 250
Why will contractors select 230.85(3)??? Well, if it involves a service upgrade on an older dwelling with 3-wire dryer and range branch circuits, option 3 allows the installation to have a 3-wire between the Emergency Disconnect and the Service Equipment, thereby allowing the 3-wire dryer and range branch circuits to stay.
There does not seem to be any hazard associated with the installation. But the language does appear to require a GEC to the GES at both switches.
The 230.85(3) Emergency Disconnect labeled NOT SERVICE EQUIPMENT now requires a Service Disconnect after either outside or inside nearest the point of entrance...which also requires a GEC connected to the GES according to article 250
Why will contractors select 230.85(3)??? Well, if it involves a service upgrade on an older dwelling with 3-wire dryer and range branch circuits, option 3 allows the installation to have a 3-wire between the Emergency Disconnect and the Service Equipment, thereby allowing the 3-wire dryer and range branch circuits to stay.
There does not seem to be any hazard associated with the installation. But the language does appear to require a GEC to the GES at both switches.