Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
From NEC 210.23 (B)
We know that if a circuit supplies either or both lighting loads, cord and plug utilization equipment not fastened in addition to equipment fastened in place, then the fastend in place equipment cannot exceed 50% of the circuit rating (breaker size determines circuit rating)
If a utilization equipment not fastened in place is hooked to a circuit it cannot exceed 80% of the branch circuit rating
However, if you have fixed in place utilization equipments and no other lighting or cord and plug non fixed in place loads supplied by a circuit, apparently either equipment can exceed 50% of the circuit rating with total load not to exceed 100% of the load.
For example 2 fixed in place appliances on a 20 ampere circuit. One at 19 amperes and the other load at 1 ampere, for 20 ampere total load.
I thaught circuits (breakers) in general were not to be loaded over 80% of their rating but my NEC hand book says:
"The requirement does not apply to a branch citcuit that supplies only fastened in place utilizatiin equipment. For example, a 20 ampere branch circuit that supplies a waste disposer and a dishwasher, neither appliance is restricted to 50% (10 amperes) of the branch circuit rating. The combined load of the two appliances cannot exceed 20 amperes" page 119 nec handbook 2023
i disagree and belueve the circuit should be limited to 20 i amperes x 80% = 16 i amperes