"multiwire branch circuits shall supply only line-to-neutral loads" Isn't the line running to a water heater a multiwire, and a line-to-line load. I don't understand.:smile:
A MWBC serves as multiple 120v circuits. A 240v-only load does not use the neutral, so it's not a MWBC."multiwire branch circuits shall supply only line-to-neutral loads" Isn't the line running to a water heater a multiwire, and a line-to-line load. I don't understand.:smile:
A MWBC serves as multiple 120v circuits. A 240v-only load does not use the neutral, so it's not a MWBC.
And some 240 v units that use a neutral, as a dryer, would not be a MWBC.
210.4(C), exception says otherwise.![]()