It is not a multiwire branch circuit, and yes it is a line-to-line load.

From Article 100; Definitions:

Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

kent
 
Well that makes 2 of us ??????????????? Maybe you could give a little more information to understand what you are asking.
 
"multiwire branch circuits shall supply only line-to-neutral loads" Isn't the line running to a water heater a multiwire, and a line-to-line load. I don't understand.:smile:
A MWBC serves as multiple 120v circuits. A 240v-only load does not use the neutral, so it's not a MWBC.
 
A circuit can have more than one wire; many do. I suppose that makes it a multiwire circuit, in that it is a circuit with multiple wires. But the NEC has a specific definition (see post 2 above) for a THREE WORD phrase, "multiwire branch circuit." A 2-pole breaker serving a 240 volt water heater does not meet that definition, so it is not a "multiwire branch circuit."
 