There is definitely an outlet missing in the drawing, but as long as the doorway is not much more than 3' wide, you could probably substitute an outlet right near the hinge side of the door.Can you review the attached sketch, and let me know if a receptacle required at the location shown? (Though, I do not see any use for a receptacle at this location I believe one is required per NEC)
It's going to depend a lot on AHJ interpretation. A strict interpretation will require the receptacle.There is definitely an outlet missing in the drawing, but as long as the doorway is not much more than 3' wide, you could probably substitute an outlet right near the hinge side of the door.
In fact, if you shift all of the receptacle in the room clockwise, starting with a six foot space by the closet and 12 feet between receptacles, you could tuck that last outlet neatly behind the door and not need a larger number than what is in the drawing.
Their positions would not be nearly as useful, but as a exercise it would seem to fit.
It's going to depend a lot on AHJ interpretation. A strict interpretation will require the receptacle.
There is definitely an outlet missing in the drawing, but as long as the doorway is not much more than 3' wide, you could probably substitute an outlet right near the hinge side of the door.
In fact, if you shift all of the receptacle in the room clockwise, starting with a six foot space by the closet and 12 feet between receptacles, you could tuck that last outlet neatly behind the door and not need a larger number than what is in the drawing.
Their positions would not be nearly as useful, but as a exercise it would seem to fit.
210.52(A)(2) Wall Space. As used in this section, a wall space shall
include the following:
(1) Any space 600 mm (2 ft) or more in width (including
space measured around corners) and unbroken along
the floor line by doorways and similar openings, fire-
places, and fixed cabinets
How could either of these solutions comply with 210.52(A)(2)?
It works first outlet behind door in 2.5 wall second going clockwise moved to 6 instead of 4 etc
Depends on how you read the section.How could either of these solutions comply with 210.52(A)(2)?
The spot in question is surrounded by doors and is larger than 2' that means it must have a receptacle there.
Wow ...
Talk about taking the exceedingly simple and complicating the heck out of it.
The rule is to prevent cords across door ways.
If so, is it the same hallway as the one on the other side of the door, outside the room?If the closet is built in, using normal wall construction, why couldn't this 2.5' area be considered a hallway?
I would say not, a doorway is a common differentiator for hallways. But it makes no difference to my 'brainstorming', does it?If so, is it the same hallway as the one on the other side of the door, outside the room?
I would say not, a doorway is a common differentiator for hallways. But it makes no difference to my 'brainstorming', does it?