NEC 230.82(5) for SPDT Manual Generator Transfer Switch

Status
Not open for further replies.

Bjenks

Senior Member
Location
East Coast of FL
Trying to determine if I can use NEC 230.82(5) which referenced Taps can be used on the supply side of a disconnect if used for a standby power systems. I have an EC who has a bank customer who has a 800A 3 phase service and want to put a connection in ahead of it so they can manually connect a temporary generator if needed. He wanted to install a SPDT switch in that would either have the utility supply the load or the generator (the generator breaker would be isolated N-G). I said no he would have to install something upstream that has OCPD for the utility in it, create a N-G connection, run a ground to the existing service, isolated the N-G in the existing service panel. Now I am reading NEC 230.82(5) and wonder if I was wrong? Or Maybe that is referring to a tap that feeds another service rated ATS that also has a normal supply OCPD such as I would do for a fire pump?
 
I would put it after the main disconnect and float the neutral on the generator so you can use a 2 pole transfer switch with appropriate OCP. I don't really see any advantage to putting it on the supply side of the main and I don't know if that is allowed. If you bond the generator neutral, it would require more work than using the main panel neutral bond and GEC. You would need a 3 pole transfer switch as well as a GEC to the generator. Does he want to use a manual transfer switch so he can do the load shedding manually rather than an ATS with a sub panel for the circuits that will use the standby sysyem?
 
The banks main disconnect is actually part of the switchgear for the building so you really can't put it after the main disconnect in this case. Sorry I didn't explain what type of disconnect is existing. Also this was just one example of many other situations that come my way where someone is trying to put a whole building generator on an existing service. So I am specifically focusing on applying NEC 230.82(5).
 
Your switch, whether manual or automatic, needs to be rated for use as service equipment since it takes a POCO input without upstream OCPD.
 
Your switch, whether manual or automatic, needs to be rated for use as service equipment since it takes a POCO input without upstream OCPD.

Rabbit trail alert: Just want to address this as I have had several EC who believe they can put a non-OCPD ATS in front of an existing main OCPD breaker service electrical panel only because it is service rated. I do not believe that is true and they seem to be surprised when I tell them that. In order to use the ATS as service equipment it needs to have a main breaker in the normal supply of the ATS or something upstream (making that the SE and not the ATS). Now if we are talking about a DT non-fused switch reading 230.91/.94 and this thread it seem you can use it as the service disconnect if they are basically mounted right next to each other. http://forums.mikeholt.com/showthread.php?t=165357&page=4 I will say this was an enlightening thread
 