Bjenks
Senior Member
- Location
- East Coast of FL
Trying to determine if I can use NEC 230.82(5) which referenced Taps can be used on the supply side of a disconnect if used for a standby power systems. I have an EC who has a bank customer who has a 800A 3 phase service and want to put a connection in ahead of it so they can manually connect a temporary generator if needed. He wanted to install a SPDT switch in that would either have the utility supply the load or the generator (the generator breaker would be isolated N-G). I said no he would have to install something upstream that has OCPD for the utility in it, create a N-G connection, run a ground to the existing service, isolated the N-G in the existing service panel. Now I am reading NEC 230.82(5) and wonder if I was wrong? Or Maybe that is referring to a tap that feeds another service rated ATS that also has a normal supply OCPD such as I would do for a fire pump?