Ever install an extra outlet not required? Do we install code minimums on small welder circuits or measure out every foot allowed for length?
Encountering HVAC contractors refusing to warranty residential equipment until client installs appliance-surge protection. Since listed surge-outlet warranty's require whole house surge protection, client end up paying for both, plus any CSST bonding corrections identified by EC, who can't compel HVAC contractor to correct anything without a Red Tag.Very true, but that extra bonding is not the responsibility of the electrical contractor...it is the responsibility of the contractor that installed the CSST. That contractor can either install the NFPA 54 required bonding or hire the EC to do it.
Must be a regional thing. Did all the smart and sensible folks move away?I guess I can spoon feed this.
While in theory this is true I cant recall seeing a compliant install lately involving a dryer . Some cant even use a cord connector let alone wire them right.
A 10AWG wire to a gas line isn't going to do anything to make that safer.Found an electric water heater 2 days ago not grounded, had a green and a white, both taped off but hooked in the panel.
What you said was,Secondly,,, cant see where I said it was a code requirement other than the language that it be grounded for the largest circuit that would potentially energize it. While it is connected by a 15A circuit to the furnace with a 15 wire there are 30 other 20A circuits in the place.
And then went on to clarify,"One I did the insp was a fill in guy just before he became the head nut. Pretty worried about the 4 to the water system but seemed to think the 15A wire to the gas pipe was adequate. It might be an irrational fear but I like the 10 better."
"This was not with the circuit conductors but a separate bond to the piping."
Metal water pipes have different bonding requirements than gas piping.Lets say we have copper water pipe in a house with 20 and 30 circuits but the feed is plastic so it doesnt have a 4 running to it,,, what wire is required to bond it? Would be upsizing this connection be some kind of violation?
I don't know how you would do that. Whatever it is you are trying to say would be easier to understand if what you said made any sense.Ever install an extra outlet not required? Do we install code minimums on small welder circuits or measure out every foot allowed for length?
How are the requirements different if its not being used as a grounding electrode?Metal water pipes have different bonding requirements than gas piping.
Okay. Use whatever size wire you want.My personal prefference is a 10,,, again in case we missed this, didnt say it was a code requirement but I like it as its more robust and fits lugs well.
I have no idea what this means.I said that in the first post, included all those elements but we can seem to come up with some logic as to why that is a problem?
They are different in sizing and location. Also, the language that allows a gas piping system to be bonded by the circuit that is likely to energize it doesn't apply to water pipes.How are the requirements different if its not being used as a grounding electrode?
You can but it's a waste of materials.So where does any of that say we are not allowed to use a better wire?
Where did anybody say anything about where you want to make the connection? You seem to be arguing that the egc for the circuit likely to energize the piping is not sufficient.Did I try to argue a point about where to connect the wire? Imply that normal connection with the circuit was not compliant?
What makes the wire better?So where does any of that say we are not allowed to use a better wire? Or even prohibit another wire along the way?
EGC's don't go to uffers.A larger conductor is not a better one? Not more durable or subject to less v drop? Why do we upsize egc to uffers?
Where do you stop? 500MCM is a lot more durable than 10.A larger conductor is not a better one? Not more durable or subject to less v drop? Why do we upsize egc to uffers?