i get R(copper) = 0.00036You said the foam board is R10. If I looked up and converted from metric properly, the R value of copper per inch is 1/2700. So the R-value of 24 in of copper is about 1/100, i.e. the copper is on the order of 1000 to 10,000 times better thermal conductor than the foam.
copper is 4.01W/cm*K from 25-225C, = 2782.18 BTU inch/ht *ft^2*F
1/2782 = 0.00036
so yep, R total from center is 0.00864. but remember, we are not producing heat just at the center of the wire, exothermic heat density is uniform along the whole wire given that ohms/inch is exactly the same everywhere. we are generating heat even in the wire that is exposed to ambient, so although copper is a good conductor of heat this is not a simple heatsink model. you would also need to do the analysis of heat transfer from the internal copper wires up to the sheath and then to air. for these several reasons i do not believe the exposed ends have any significance to the temp measurements being taken at the center of the wire.
my ambients were taken using IR gun (whole degree display), which was about on par with my CM660 TC sitting in ambient for an hr or so (IR gun was showing couple degrees colder than the CM660 TC probe). i can get a faster read with IR gun than the metal TC probe.