I haven't look at the N&M equations, but basic physics says for a unit length of wire of diameter d and _surface_ area A
P = I^2 * R
R varies as 1/d^2
So P varies as I^2/d^2
A varies with d
So P/A varies as I^2/d^3
Temperature rise of the wire should be an increasing function of P/A (power dissipated per unit surface area of the conductor). Certainly that is true for the radiant and conductive components of heat loss, not sure about convection. So at least to a first approximation, a given maximum temperature rise will mean a fixed maximum P/A.
Thus there's nothing linear here: ampacity should vary as diameter to the 3/2, or cross-sectional area to the 3/4. How does that compare to the trend in the NEC ampacity values?
Cheers, Wayne
sure, but the ohms/100ft tables for AWG sizes are already done, i simply took those R values, etc. the P for each of those using the NEC ampacity table is not constant. why is that? P has to dissipate somewhere. if XYZ wire generates 10w then its 10w (10J/sec) of energy that has to go somewhere, and this has temp associated with it. if N-M equations show that temp rise is not directly proportional to P in linear fashion for varying wire sizes then this may explain it, but i just didnt see it in the N-M equations. NEC tables list ampacities that shows an increase of P density (heat generation) as wire size gets bigger, etc.