- Massachusetts
Interesting, yes. More interested if this was uncovered in a house or cobbled up in a studio somewhere.
Or the other facts, like loading etc.
pinched the pvc on the inside?? i dont think a plastic zip around that diameter would have enough force to damage the pvc on the inside. cant know for sure unless there was some forensics done on that bundle. but heck, its one of this scenarios we want to avoid, but can be addressed outside of ampacity, possibly through derating, or just blatantly not allowed (perhaps a starfish holder would be allowed, holds many nm's together whiles keeping a space between them). and seems odd that only that small section was bundled, perhaps that was a test setup?
a NEMA article, just not sure when it says "temps were never objectionable" if that is applied to testing installations that were derated, or, if the bundled wiring was tested at full ampacity w/o derating.
https://www.nema.org/Technical/Docu...Spray-Foram Insulation Used in Residences.pdf
...i am want to see the evidence as to why NEC changed it...... and why NEC has the 15A OCD restriction.
I have been doing this work for more than 30 years now and I have never once wondered or concerned myself about the NECs choice of ampacities.
It's not just you. Debating and discussing ampacity is an exercise for engineers and people with a lot of free time on their hands. I've said it many times and will say it again - we have a good system here that has worked for a long time now.
Most likely the NEC did not perform any of these analysis for their Small Conductors.
Their 'restrictions' are likely not much more than feel good values that address cable construction, conductor insulation and installation considerations over the past 100 years of electrical installations. As such the report values bear no relationship to real world physics.
Your deep dive analysis may be more germane to equipment standards, like those that allow #18AWG in fixtures.
The OP is certainly a valid inquiry. On the other hand, as my favorite code instructor once said "This book is written in blood" I think often that is a good enough answer. On the other hand, I too question the rationale for certain things in the same way ya'll are - I think it is good to do so and can be very educational. On the other hand, I think one could go in circles for a long time and arrive at the same basic model we have now.Its built into the numbers and codes themselves.
so my point is, if its insulation damage from heat that NEC is trying to protect against, then use a std based on watts/area, or watts/ft of wire to define ampacity and OCD #'s.
but ok, thats for the older insulation types, what about wire rated at 90C but has terminations rated 75C, why still restricted to 15A OCD ?? seems less to do with failing insualtion and more to do with heat generation. the Gexol insulation can run real hot w/o issue, so when will NEC add a 110C column? are ampacities based on insulation damage by temp, or just generation of heat? seems to be the latter given insulation like Gexol is out there. sure, terminations are still not common in 90C, but you get my point.
IMHO and based on experience insulation damage due to heat is probably at the bottom of the list of concerns. I would think that heat buildup at connections, devices, and panelboards is probably more of a factor.The UL489 standards limit the standard molded case circuit breaker terminal temperature rise to 50C when loaded to 100% in an open air ambient temperature of 40C.
Which seems to say that at 100% loading the conductor internal heat generation is limited to a maximum of 50C, not the ultimate rating of its insulation.
For example last spring I uncovered a ground fault in a 4" sq metal box, everything wired to code, where the ungrounded conductor burned a hole through the back of the box and charred the wood behind it. It was a 277V lighting circuit with #10 THHN running about 300ft fed by a Siemens model BQD 20A breaker. (CCC's were oversized due to voltage drop.) Complaint was that breaker would trip occasionally. Upon inspection I found that it took about 3 seconds on a dead-short to trip the breaker, no doubt due to voltage drop limiting the fault current. If careful, one could weld with it and not trip the breaker. Definitely not a safe scenario.
I can only imagine what would happen if this were a 14-2 NM running a long distance and a non-metallic box. Perhaps an EE could calculate fault current on 500ft distance and apply that to time-current curve of different OCPD sizes, and see how safe you really feel about NEC ampacity tables or changes to it.
this can be addressed via verbiage on wiring and not by ampacity. there is nothing verbiage can do to protect against a hazard if the wiring is not to code and/or faulty, etc.
i suspect you mean the additional ohms of the long run and not "voltage drop" since all of our OCD items are current based.
Old thread about thermal insulation: http://forums.mikeholt.com/showthread.php?t=162956&highlight=
Understood, clearing a fault is different from continuous load ampacity that you're addressing. I believe this is germane to the conversation because it could play into the NEC sizing req for the smaller sizes, all I'm saying is it's something worth considering.
Correct it isn't really voltage drop but the high impedance resulting in lower fault current resulting in more time elapsed before OCD clears - which is really the bottom line - open circuit before starting fire.
The amount of energy at point of fault is still enough melt wires and steel, so given enough time (seconds) has high probability of starting a fire vs. near-instantaneous trip with shorter runs. When it comes to sizing conductor vs. OCD I think this is an important factor that should be considered but isn't really addressed in the code (or is it????)
Maybe I'm crazy and this shouldn't be a concern?
#14 at 2.6 Ohms per 1000ft on a 500ft run = 2.6 ohms total. 120V/2.6 = 46 amps. A standard GE THQL1115 breaker, 15A, would take 5-30 seconds to clear. That's a long time of arky-sparky.
#14 on a 20A breaker would be 12-90 seconds, quite a bit longer.
#12 at 1.6 Ohms on a 15A would clear in 1-9 seconds, still too long but much better.
#10 would clear in less than 3 seconds.
All I'm saying is with no voltage drop sizing rules to prevent extended fault-clear times, NEC would really be going out on a limb to increase ampacities of smaller sizes vs. OCD size.
interesting article. i would still have some Q's around their conclusion that the insulation allowed the temps to rise so high that thermal damage was done. almost seems like the original wire may have been faulty, some arc'ing occured, and then finally full failure.
this leads me to ask another Q. how many electricians are derating for wire that runs in attics where the attic has no roof line insulation? i ask because most attics like this get well above 30C in summer. as example, my own home panel is outside, all wires run up the garage wall and into garage area attic (nothing is insulated in this area. summer time the attic there gets fairly hot and there is no venting). from what i can see there was no derating done.
and, did i miss it. NEC OCD sizing is not applied after wire derating ??
What you posted is pure diamonds trumping what I posted above.Man my brain is in sensory overload tonight :lol:
Thank you for the kind words, especially given the high standards on this forum.
One problem I had with that publication is that they kept talking specifically about foam insulation. The whole point of having R values is that they allow comparing apples to oranges by measuring total resistance to heat flow. At any given R value, a priori it shouldn't matter whether the heat is building up behind foam, behind cellulose, or behind recycled shredded blue jeans. The temperature rise should be the same in all cases.