- Massachusetts
But somehow electricians get to pick and choose if they comply with 110.7
No idea what that sentence has to do with my post or 110.7.
Ok, how many electricians actually perform tests to verify 110.7?
That section does not require any testing, it only required the work be free from shorts.
While obviously I cannot hit every possible thing, I am trying to make a checklist up for our inspectors to look at when inspecting wiring and conduit inside of small control buildings. The work is relatively minimal, so I am don't need anything elaborate. Just curious if anyone has some advice on things to add, or maybe an inspection sheet of their own they would be willing to share.
Things like tying all the grounds that run through a metal box to the box. Simple things to look for that are going to get us nailed when the local inspector takes a look.
Or securing conduit.
Little things that are real obvious to people in the trade for 20 years, but maybe not so obvious to others.
But how do you know that without testing?
Because I am just that awesome.
It really depends on the work at hand. A big feeder I do some simple tests before energizing.
But typical branch circuits no we don't test them. We turn them on.
Awful example. Voltage drop will not burn down a home. Damaged insulation can, and we all know breakers have limitations. An IR test would catch this. And by IR I mean insulation resistance, so don't even try that trick![]()
If it makes a big bang or blows up in your face when you put it on line - it has a problemBut how do you know that without testing?
If it makes a big bang or blows up in your face when you put it on line - it has a problemhmy:
When it comes to safety we need to identify the problem before we start trying to provide a solution.
We could do insulation resistance checks (megging) on new residential contruction but would it be worth it?
Sure there are conductors damaged by sheet-rock nails and screws or siding nails but where is the demand to change the system. How many fires will be prevented by insulation testing?
We could all wear a crash helmet while driving around town or even body armor and sooner or later it would prevent a death.
:thumbsup::thumbsup::thumbsup:
That might be a new signature for me.
I came up with a draft of my checklist. Maybe some people would be willing to take a look and comment.
GENERALLY, 3 FEET OF WORKING SPACE IS REQUIRED IN FRONT OF ELECTRICAL
EQUIPMENT AND 3 FEET SIDE TO SIDE. I THINK THE CEC EXTENDS THIS TO 1 METER.
THE WORKING SPACE EXTENDS FROM THE FLOOR TO A HEIGHT OF 6.5 FEET.
CONDUIT AND OTHER EQUIPMENT ASSOCIATED WITH THE ELECTRICAL
INSTALLATION CAN EXTEND NO MORE THAN 6 INCHES PAST THE FRONT OF THE
EQUIPMENT. NOTHING ELSE IS ALLOWED IN THE WORKING SPACE
shouldn't that be 30 inches?
404.2(C) SWITCHES CONTROLLING LIGHTING LOADS.
WHERE SWITCHES CONTROL LIGHTING LOADS SUPPLIED BY A GROUNDED GENERAL
PURPOSE BRANCH CIRCUIT, THE GROUNDED CIRCUIT CONDUCTOR FOR THE
CONTROLLED LIGHTING CIRCUIT SHALL BE PROVIDED AT THE SWITCH LOCATION.
I.E - IF THERE IS A GROUNDED CONDUCTOR ASSOCIATED WITH THE LIGHT, THAT
CONDUCTOR HAS TO BE BROUGHT THROUGH THE SWITCH BOX.
Doesn't 404.2(C) 1 and 2 negate the need for the neutral at the switch if accessible? or in EMT?
Without knowing the condition of the circuit and in turn compliance with the code...