hhsting
- Glen bunie, md, us
- Junior plan reviewer
Does anyone here know of 2 pole, 3 wire receptacle with GFCI , 120V? I have RTU and its receptacle is spec like this
It sure does... hmm.. I don't like it. hahaha.From the link that I posted it clearly states 2 pole, 3 wire.
Ever look at plug/receptacle selection charts? They often classified that way.That seems like a weird way to have it spec'd. Is that from the factory or designer? Although I agree with hillbilly1's statement, i don't like the term 2-pole for a 120v circuit. and 3-wire... if they are talking about Black White Green(bare) okay.. but that is like a homedepot phrase IMO.
OP needs to clarify. Kind of indicates it says 2 pole 3 wire, 120 volt. But then adds the question mark and we not really sure if he is quoting or asking.OP set 2pole and ask if that is 120v
If that is 2 pole (208-250v)regular receptacle 120v is no good and needs GFCI disconnect or GFCI breaker
2 pole 3 wire, 120 volt (proper should be 125 volt) would be 5-15, 5-20, L5-20...
2 pole 3 wire 250 volt would be 6-15, 6-20, L6-20...
OP doesn't state voltage other than 120 followed by a question mark.
Also would be very rare for a RTU to require a cord and plug connection adding even more questions or confusion here.
Could be, like I said some clarification is needed because what was described isn't all that typical assuming it means what it appears to say.The receptacle is probably for servicing the RTU as required by code. As for two pole 120, remember code considers the neutral a “hot” wire once it leaves the service.
I agree with all of whats being said... but Infinity made the clearest point in his 1st post with the link. The link clearly states in the specifications that the GFCI receptacle is 2 pole, 3 wire. damn terminology hahahaCould be, like I said some clarification is needed because what was described isn't all that typical assuming it means what it appears to say.
There is no contact for the EGC?2 pole = 2 contacts. I don't understand the confusion.
Two pole three wire means two current carrying and one grounding conductor
Three pole four wire means three current carrying and one grounding conductor
Three pole three wire, non grounding would be like the old three wire range and dryer receptacles.
Got it, you were only referencing a GFCI receptacle and referring to the contacts that open within the device when activated.