You wouldn't happen to have a code reference for the number of receptacles on a circuit would you?
I don't know your Code that you are working out of. My answer is based on the 2014 NEC. The basic reference is to 220.14(J).
Consider the house in your opening post. To figure out the 2014 NEC minimum wiring configuration we follow specific guidelines for receptacles, luminaires and switches as laid out in 210. However, for sizing the service and arriving at the minimum number of circuits, we do the calculation laid out in Article 220.
Start with 220.12 to see the requirement to measure from the outside dimensions of the dwelling when calculating floor area. The informational note to 220.12 taken with 90.1(B) says that the calculation may well end up with a Premises Wiring (System) that the homeowner will not find adequate, and that is OK because it will be "essentially free from hazard." Note the floor areas described in 220.12 that don't have to be included in the dwelling total floor area.
The rule of 220.12 refers you to Table 220.12 where you will find the General Lighting Load requirement to be 3 Watts per square foot. Considering the house you describe in your opening post (OP) multiply the calculated square feet by 3 Watts per square foot to get the Wattage of the General Lighting Load. This is a minimum amount required by the NEC for your specific house. Lets say your house has 1500 square feet by calculation from 220.12. 3 Watts/Sq Ft times 1500 Sq Ft = 4500 Watts.
NOTE: The line name "Dwelling unit" in Table 220.12 has a superscript "a". Follow the superscript "a" to the bottom of Table 220.12 and you will read "See 220.14(J)".
In reading 220.14(J), to me, the most important phrase is "No additional calculations shall be required for such outlets." 220.14(J) (1), (2) & (3) take a while to read and understand the specific outlets that are included under 220.14(J).
Now, here is where we work back to the number of Outlets allowed on a General Lighting Load branch circuit in your OP house. A 20 Amp 120 Volt over current protective device lets through 2400 Watts. How many 20 Amp branch circuits will provide a minimum of the 4500 Watt calculated General Lighting Load in your house? The answer is: divide 4500 by 2400 and round up to the next whole number. The result is "Two". Two 20 Amp 120 Volt branch circuits will provide the MINIMUM amount of power for the "General Lighting Outlets" described in 220.14(J) for the 1500 Sq Ft of your house. In your case, dividing 1500 Sq Ft by 2 circuits yields 750 Sq Ft per 20 Amp General Lighting branch circuit.
For your house that you ask about in the OP, let's consider the floor area of the bedrooms, bed closets, hallway, living room, etc., summing them to a total of 750 Sq. Ft. In these areas, all the General Lighting outlets present (as required by Article 210) are the MINIMUM number of outlets that can be on that one 20 Amp General Lighting branch circuit of 20 Amps.
When I get to this point, I can see that 750 Sq Ft is a large area, and, in the bedrooms, and similar areas, there are no other branch circuits that are REQUIRED (like the Small Appliance branch circuits, or the furnace circuit, laundry circuit, etc.). Pretty much ALL the outlets present need only be supplied by the minimum number of calculated General Lighting Load circuits.
There is no fixed "receptacle" max count per circuit for a Dwelling General Lighting Load branch circuit.
I, personally, find it pretty easy to add an additional branch circuit or two, to split up the 750 Sq Ft area into smaller areas but that is a design choice of mine and is not required by the minimum of the NEC. If the person or business that is paying me only wants the absolute minimum wiring package, this is how stripped down and bare the Premises Wiring (System) can be. As 90.1 says, it may not be "adequate".
I have seen that position before, but NEC does not require that.
What do you find the NEC to require in "that position"?