Per the NEC the EMT is adequate as EGC. If this is not to your liking or you feel is a safety concern write a proposal for the code panel(s) for it to consider a modification to the code. I can understand your rationale, and it is your perogative to install a wire type EGC but it currently not required under the NEC.
I don't believe his skill level is necessarily above an "average electrician", there is installation criteria that must be met by every electrician and if not met they are not "average" but less than average.
There had already been referenced studies on the capacity of use of EMT as a grounding conductor and was adequate. And the code has very specific installation criteria for use of the metal wireway or conduit as a EGC, some such as restricted use of concentric KO by requiring bonding bushings on the the connections, clean connections (removal of paint or insulated materials), etc.
If connections are failing inadequate consideration of potential expansion, vibration, moisture, etc was made during instalation.
I understand that. The company I used to work at never practiced that at all. It had nothing to do with anyone not being able to adequately run conduit, it was a safety measure. I can’t guarantee that my helper or anyone under me has fully tightened every connection to the satisfaction of code requirements to use EMT. Even if you did tighten them, there’s always the ones that feel tight but always work loose or never could’ve been tightened in the first place. Besides that you have metal boxes you’re running circuits through that have concentric knockouts on them (1/2-3/4 and 3/4-1), are grounding hubs used on them as well?
i get why people may want to exercise that option to use EMT, however some of these guys have come across arrogant in their response. All I’m saying is I can’t guarantee in anything I do that an outside factor won’t cause my fittings to loosen even a tiny bit and subsequently cause someone to get hurt in a failed and grounding out circuit situation. Besides that, I have 8500 students that I need to keep safe. Many of these older housing units have conduit that is in concrete and I can’t guarantee the efficiency of being an adequate EGC. I see no reason to test each and every conduit versus just pulling a green and bonding the boxes.
In this situation I’ve outlined here, there are over 200 units done this way. I will bet my salary that the contractor that did this upgrade never tested each conduit run back to mdp to verify yea this one will work but no this one won’t. It was a game of assumptions and the cost of an additional wire was omitted based on meeting the minimum code requirements.
Nothing is outlined on upgrades per the code requirements. It is left up to the contractors to do what is allowable but there’s no follow up or inspections and they know that and therein lies the issue of barely getting by at best. I’ve found multiple violations every where I look because no one care about code, they just got the job done and left. If anyone could see the pic, they’d see a grounding bushing was used on the panel and #6 phased green was jumped down to the ground bar. So when looking at that, I’m going to assume nothing this contractor did was to code if they can’t make a jumper that’s not a violation of nec code on phasing the green.
It’s a simple matter of just adding a wire to your estimate and setting yourself to pull it. What’s the cost of a ground when compared to feeders and circuits? How minimal is it to just to take the extra step to avoid future maintenance testing?
April of 2019 in Dixon, CA two boys electrocuted because a bridge was energized due to a faulty ground
in reading older articles posted on this forum, using EMT has been brought up multiple times. Many of you guys commenting here were posting in that thread. There was more mention of distance being a factor and also building steel supporting conduits but it was also mentioned about how the paths can fail which causes a possible issue.
Big john said “but I will concede that when designing a circuit, the electrician can’t depend on that, so it should be wired for worst case scenario”
My exact point. These conduit runs aren’t mapped out and once they disappear in the concrete you have no idea where they go, how they’re run and how effective they are at being an EGC and I’m positive there was never a test done on their ability to be a proper EGC.
if anyone wants to use that method, more power to you. It’s within your right. However it’s also within my right to use a wire to heir on the side of safety. I can’t risk the safety of the staff and students because of my ego over my conduit running abilities