electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Feeder neutrals only need sized per the load they will carry, but in no case can be smaller than the required EGC for that circuit. So 600 amp OCPD means 1 AWG copper or 2/0 AWG aluminum is absolute minimum neutral you can run with that feeder. I have done this before. Did this for a 600 amp feeder supplying a panelboard that served several three phase HVAC units. In addition to those units there was a 15 amp circuit supplying lighting in the vicinity, a 20 amp circuit supplying a 5-15 receptacle for servicing the units and two other 15 amp 120 volt pieces of equipment in that area. Total neutral load probably less than 30 amps - still had to run 1/0 aluminum
I did recently too. Existing 200A 3 wire feeder in 2"EMT.
Pulled in a #6 neutral and a #6 EGC. Couldnt get a snake thru, had to pull apart the pipe at a 90 near the middle to make an intermediate point, went fine from there. Rooftop panel serving a bunch of RTU's, just needed neuter for my service receps and maybe a few outside lights.