frizbeedog said:I call it a grounded conductor. After reading through all this I came
to realize that it may be understandable for some who have been in the trade for a time
but the concepts and the terms make it difficult to explain to our students. And I think
that this is your concern.
So I went looking....and found this.
When a 'neutral' isn't a neutral
Good article
The only thing I see I disagree with is to be a neutral it says anything tapped midpoint.
It doesn't mention polarity. To operate like the true Edison neutral and to balance out the
polarity has to be opposite at the neutral point to balance. In other words at the neutral
point you need to have a positive and a negative. Not two positives or two negatives.
In the real world of working with wye three phase and the Edison single phase this is
always the case so Electricians don't need to worry about that.
But in the Electronics design this might not be the case so the designers would need to
watch for polarity if he wants the circuit to balance for some reason. .