To summarize, my understanding is that the code allows either
1) SBJ at XF and no SBJ at both disconnects, with SSBJs run to both disconnects
2) SBJs at all three locations, with neutral (and no SSBJ) run to both diaconnects..
There are two problems with OP's description of situation:
First, no SBJ at XF, which is required.
Second, SWB was done according to (2) above, and fire pump was done according to (1), which results in objectionable neutral current on the fire pump SSBJ if both disconnects are grounded to the building GES as required.
The fire pump and SWB can be done either way but must both be done the same way to avoid the objectionable current.
If the description is of what is already installed, I hope that 'EGC' is large enough to be a black wire that can be retaped white and satisfy table 250.102(C)(1).
1) SBJ at XF and no SBJ at both disconnects, with SSBJs run to both disconnects
2) SBJs at all three locations, with neutral (and no SSBJ) run to both diaconnects..
There are two problems with OP's description of situation:
First, no SBJ at XF, which is required.
Second, SWB was done according to (2) above, and fire pump was done according to (1), which results in objectionable neutral current on the fire pump SSBJ if both disconnects are grounded to the building GES as required.
The fire pump and SWB can be done either way but must both be done the same way to avoid the objectionable current.
YES fire pump controller 3 phase, 3 wire fed by the transformer secondary feeder with EGC and no neutral.
If the description is of what is already installed, I hope that 'EGC' is large enough to be a black wire that can be retaped white and satisfy table 250.102(C)(1).