Per 220.61(C)(2), I think that you shall not reduce the neutral on any 3P,
4Wire system--on the portions where there are non-linear loads.
Since many, if not most, 3P commercial/industrial loads are non-linear, I've never reduced the neutral in such a situation. Many times in recent years the engineering specs. an increased neutral sizing.
Even electronic lights ballasts usually only have 10% or 20% THD, so I wouldn't even consider those nonlinear.
Steve
Karl, are you saying that if I have motor drives (3-p) and some L-N loads, and I'm putting in a 200A panel, that I have to size the neutral for 200A? That's not what I was understanding Charlie to be saying.
I've had to deal with some neutral overloading problems due to non-linear loads. One of them was in a very up-market hotel in the Middle East where a substantial proportion of the load was non-linear single-phase.Some computer and receptacle loads may be non-linear, by I don't think there are enough to worry about in a typical office building. I think manufacturers have blown this issue out of proportion in an attempt to sell more expensive stuff. And many engineers have jumped on the bandwagon.
I'm not saying non-linear loads are never a problem, but its just not common enough to apply to an average service or feeder.
Even electronic lights ballasts usually only have 10% or 20% THD, so I wouldn't even consider those nonlinear.
Steve