There has never been a requirement that the neutral/ground and equipment ground bus be isolated in a panel.
There are already rules specifying the measures to be taken to ensure that objectionable (load) current does not flow in grounding (includes equipment grounding) conductors.
Objectionable current is any current other than the temporary currents which are set up under fault conditions while the grounding conductors are performing their intended protective functions.
There shouldn't be any need for another rule.
There was no need to add the fourth wire, other than to market more wire.
Bennie, I am surprised that you would make such a statement. There are many folks here that might actually think that it is accurate.
I'm sure you must remember the days before equipment grounding conductors, when ground faults in equipment didn't often trip breakers or blow fuses. I remember a lot of "live" washer and dryer enclosures.
The fact is, in terms of safety, the Equipment Grounding Conductors (ECGs) are
much more important than the Grounding Electrode Conductor (GEC) in an installation.
Ed