Re: Neutral Conductors and Equipment Grounds tied together a
X'tian: Ignore my statements. I have been accused of misleading the new people that may be reading this thread. My reading comprehension has also been questioned.
Separate the neutral/ground, and equipment ground conductors in a panel after the service. This is the commonly accepted method, except in detached buildings. You will always be correct with everyone, except me.
I have the same code book as everyone else. I also have many technical, and engineering manuals, and books.
250.24 (5) has nothing to do with a panel after the service. The text is about single point grounding. To phrase it simply; Don't stick the neutral/ground in the dirt after the service.
A panel after the service, if supplied by three circuit conductors, must have the neutral/ground, and equipment/ground conductors bonded in the panel.
When supplied by four conductors, or paths, for current flow, the neutral/ground and equipment/ground conductors must be separated to prevent parallel paths for normal load current.
By installing four wires to a panel, you are increasing the ground fault path impedance. But it is accepted by most people. On a 200 amp feeder you are changing from a 4/0 to a No. #4.
The neutral/ground, with the feeder, of a three wire cable is completing the fault path for the equipment, supplied by the panel. The reference to the neutral not being a ground for equipment after the main, is addressed to branch circuits.
It may not be clearly stated in the code book, and implies the feeder neutral/ground can not be used for grounding purposes, but it is technically incorrect.
Now everyone can question my credibility and intelligence, but show me the math and facts.