I have four wires from my meter main to a panel across my garage. The ground conductor is a #4 al. The other three are 4/0. This is a cable assembly.
If this panel was connected with three wires, ground fault current would have a 4/0 conductor for a path. Now with the new interpretation of separating the NG at a panel there is only the #4 for fault clearing. This is backwards technology and is wrong. It is not what the code says.
As a wild hypothetical: Imagine a service panel with L-1 L-2, and N buses running the entire length of the house.
All branch circuits will connect to the closest location. There is no parallel current flow, yet the fault path is short, Everything that needs to be grounded will be grounded.
This is the same thing as having a remote panel.
So why the four wires? The code does not require four wires.