The following was added in the 2011 edition of the code.
200.2(B) Continuity.
The continuity of a grounded conductor shall not depend on a connection to a metallic enclosure, raceway, or cable armor.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
But suppose you add an adequately sized neutral conductor joining the two bars, namely the added bar mounted on the enclosure, and the original neutral bar that presumably has an MBJ connected to it. That solves the 200.2(B) issue. Is there a remaining issue with having two neutral-ground connections within a service panel, the MBJ and this new neutral/ground bar's connection to the enclosure? Or is it OK?

Cheers, Wayne
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IMO: If such a "jumper" is present it would then connecting to the "grounding" bar would not be a violation of 200.2. A potential problem might be if the manufacturer identifies one bar as "grounding" then 110.3(B) could apply.
 

elkappyton

Member
Location
new jersey
Occupation
electrician
In a main panel, can a neutral wire be landed on a ground bar that was added (connected to the case).
This is a picture of the failure. “Ground bar” connected to case w/ threaded screws, neutral bonded to case with provided bond screw.
 

Attachments

  • 2BF7F9A4-70CC-4026-9DC0-BAF7C0999BEA.jpeg
    2BF7F9A4-70CC-4026-9DC0-BAF7C0999BEA.jpeg
    386.4 KB · Views: 29

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
As already stated, the added bar will need a wire jumper. The can is not a not a current carrying conductor however, it can be a fault clearing conductor
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
I'm not a fan of running a jumper from the netural bar to a ground bar within the same enclosure where the MBJ is installed. Just a personal preference.

Dislike seeing a white grounded conductor/ netural under a green screw. Especially a netural.


I personally think it would be a bad habit that might migrate to other work.

If possible I would move some EGC conductors to make room to re-land the grounded conductor/ netural to the netural bar. Maybe even add a ground bar if necessary.

I have to ask that white wire. What does it serve. Is it part of the line side tap.
 

Attachments

  • Screenshot_20230726-155010.png
    Screenshot_20230726-155010.png
    156.8 KB · Views: 3

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Similar to this discussion:

 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
If a wire was added between the netural bar and ground bar how would it be sized other than using common sense.

Go by largest hole available on the ground bar.
250.102. minimum size required for grounded conductor.
Same size as the grounded conductor feeding the panle.
If an AHJ allowed this how would they inforce sizing per NEC.
 