I believe there are listed neutral bars that can also be used for equipment ground.

My feeling likely wrong is that the typical ground bar is not meant to carry continuous current.
They are the same thing, there is no difference between a ground bar and a neutral bar. It's a piece of steel with holes drilled in it.

Can a wire nut tell if it's being used for a hot, neutral, or equipment ground?

I just don't think they have a pile of neutral bars in one bin at the factory and then they have another pile, the same size and colour, made of the same material that are for equipment grounding only.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Although some of this discussion is interesting it still doesn't seem code compliant to install a neutral on the EGC bus connected directly to the panel enclosure even with a jumper to the neutral. In doing so there would still be objectionable current flowing on the metal enclosure which is in direct conflict with the provisions of 250.6.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Although some of this discussion is interesting it still doesn't seem code compliant to install a neutral on the EGC bus connected directly to the panel enclosure even with a jumper to the neutral. In doing so there would still be objectionable current flowing on the metal enclosure which is in direct conflict with the provisions of 250.6.
It's the same when you put the required bond bushing on a service raceway.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Although some of this discussion is interesting it still doesn't seem code compliant to install a neutral on the EGC bus connected directly to the panel enclosure even with a jumper to the neutral. In doing so there would still be objectionable current flowing on the metal enclosure which is in direct conflict with the provisions of 250.6.
I disagree. Many service enclosures have the neutral bar directly connected to the enclosure so this happens anyway. The way the code requires the service enclosure to be bonded to the neutral essentially *requires* current to flow on the enclosure. It can't be objectionable current of the code normally permits and requires it.

Edit: or, what Dave said.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Many service enclosures have the neutral bar directly connected to the enclosure so this happens anyway. The way the code requires the service enclosure to be bonded to the neutral essentially *requires* current to flow on the enclosure.
That is only true if there is a metallic service raceway in which the objectionable current flow is unavoidable because service raceways are permitted to be metallic. 250.6 is very clear that if objectionable current is avoidable then efforts must be take to ensure that it does not happen.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
250.6 isn't 'very clear' at all. It's a broad and vague guidline that's fleshed out by considering other applicable code sections and the details of any installation. 'Objectionable current' isn't even defined.

I'd agree with your stance in a case where the enclosure wasn't carrying any current, say where there is a non-metallic service raceway. I.e where it actually makes a difference. In a case where there is already a parallel path that's permitted and even required by code, i.e. where it makes no difference, I wouldn't agree.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Could having all this "Objectionable Current" floating around, be the cause of "Phantom Tripping" ?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Although some of this discussion is interesting it still doesn't seem code compliant to install a neutral on the EGC bus connected directly to the panel enclosure even with a jumper to the neutral. In doing so there would still be objectionable current flowing on the metal enclosure which is in direct conflict with the provisions of 250.6.
200.2(B) says this

(B) Continuity. The continuity of a grounded conductor shall
not depend on a connection to a metallic enclosure, raceway,
or cable armor.
So if you add a wire jumper, continuity is not dependent on the enclosure.
 
  • Like
Reactions: jap

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
That is only true if there is a metallic service raceway in which the objectionable current flow is unavoidable because service raceways are permitted to be metallic. 250.6 is very clear that if objectionable current is avoidable then efforts must be take to ensure that it does not happen.
But both art. 200 and 230 are clear that an un-insulated neutral are allowed so I don't see an issue with a jumper wire to a buss.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Although some of this discussion is interesting it still doesn't seem code compliant to install a neutral on the EGC bus connected directly to the panel enclosure even with a jumper to the neutral. In doing so there would still be objectionable current flowing on the metal enclosure which is in direct conflict with the provisions of 250.6.
That’s the lines I was thinking on but I totally get what others are saying.
 