elkappyton
- new jersey
- electrician
In a main panel, can a neutral wire be landed on a ground bar that was added (connected to the case).
200.2(B) Continuity.
The continuity of a grounded conductor shall not depend on a connection to a metallic enclosure, raceway, or cable armor.
This is a picture of the failure. “Ground bar” connected to case w/ threaded screws, neutral bonded to case with provided bond screw.In a main panel, can a neutral wire be landed on a ground bar that was added (connected to the case).
Not that it changes anything but why are you not including all the details when you ask a question?The white was for the line side tap for a solar install.