Thank you. Very interesting. How cool. So the neutral has a low voltage to earth but the hot has a high voltage to earth? So this is also why generally you don’t get shocked when you touch the electrode grounding conductor that attaches to the ground rod right? I know it’s bonded to the same place in the box that the plumbing water pipe is. If you were to touch a service neutral with current flowing back to the transformer on it would you be shocked, like if you opened up the box and touched that one big aluminum wire only?
I’m starting to understand that if you were to somehow touch a pipe with current and also something else that’s bonded to ground like the electrode grounding conductor you would get shocked. I think.
Thanks again for the info
Ohm's and Kirchoff's laws are at play here.
The grounded conductor is grounded because it is referenced to earth, on a utility derived system it is referenced many times - like at nearly every structure in the distribution system as well as at each individual service.
That multi-grounded conductor does have voltage drop across segments of it, all conductors have a voltage drop across them if current is flowing. This drop is usually minimal but in right conditions even just 2 or 3 volts can be enough to shock you. That risk is about as high as it gets for us humans in situations involving swimming pools or other situations where you may be immersed in a body of water and is reason there is extra bonding requirements for some those kinds of applications.
Also misunderstanding is the myth that electricity takes the path of least resistance. Electrical current takes all possible paths, but the path with the least resistance does take the majority of said current. Even with a bonding jumper across the section of pipe you are working on, you possibly have a small current pass through you if you touch the work, but the resistance of the bonding jumper is so low in comparison to you and carries such a high percentage of the total current resulting in current passing through you being so low it is not enough to cause any concern for you. Add some kind of resistance to that bonding jumper and current passing through you rises, add enough resistance and you eventually get enough current passing through you that you can feel it.