Neutral on MWBC
OHHV
I have a question that I'd like to have clarified if possible. 120/240v 1 phase panel supplying 2 dedicated receptacles with a 12/3 cable on a 2 pole breaker. 120v per receptacle with a shared neutral. My question is if each receptacle/hot leg has a load that draws 18A and they're both running at the same time, will the neutral overload?
roger
Fl
Retired Electrician
No, the neutral would have zero amps on it in this scenario.
Roger
Rewire
The neutral conductor carries the unbalanced load,the difference between A and B phase amps will be the neutral amps.
Aphase18A - Bphase18A=0A on neutral.
roger
Fl
Retired Electrician
gndrod said:
If it is a green contract, I'd use separate neutrals just in case.
Why?
BTW, In the OP's example, there wouldn't be any neutrals if two grounded conductors were used. :wink:
Roger
iaov
Rhinelander WI
Nope. The neutral only carries the ubalanced load. If one conductor was carrying 16 amps and the other 18, the neutral current would only be 2 amps.
220/221
AZ
If the circuits were on two single pole breakers and on the same phase/leg, you would have an overloaded neutral with 36 amps.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
First, a multiwire branch circuit much use two phase in order for the grounded conductors to carry the unbalanced load. If, not in your example, you hooked both ungrounded conductors to the same phase then you would overload the grounded conductor.
roger
Fl
Retired Electrician
There wouldn't be a neutral in this case and if you were using a #8 conductor it would be fine.
Roger
480sparky
Iowegia
walkerj said:
This might be silly,but would there really be a reason to wire with a "super neutral"?
Circuits with known harmonics, such as lighting on dimmer circuits, or circuits feeding large electronics.
roger
Fl
Retired Electrician
It is not silly but, it would only be necessary in very few instances where non linear loads are the majority but, this would not be the same thing as using a grounded conductor large enough to carry the combined load of ungrounded conductors on the same leg or phase.
Roger
walkerj
Baton Rouge
Roger
The former I understand, sortakinda.
The latter I dont see any reason to:-?
480sparky
Iowegia
walkerj said:
But why a MWBC sharing the same phase and a Super neutral
I'm feeling brickwallish today
If the two circuits are on the same phase, then you don't have a MWBC. You have two circuits that will overload the neutral. The definition of a neutral is one that carries the unbalanced load, not the total load.
OHHV
Thanks. I was thinking of it as both being on the same phase and that's where the confusion came from and not 180 degrees apart. The original conversation started because the electrician was running one homerun of 12/3 to two bathrooms, with a dedicated gfci in each. Can you guys also clear up the confusion that if these 2 gfci receptacles are installed using the 12/3, will sharing the neutral affect the way they operate?
Dennis Alwon
Chapel Hill, NC
Doesn't seem possible to wire with the super neutral with the 2008 code requiring a dp or a listed breaker tie on MWBC.
Smart $
Esteemed Member
Ohio
No, provided we remain in the realm of a 120/240V system...
The first thing everyone brings up is the harmonic current of non-linear loads. However, it is only the triplen harmonic currents of 3? systems that add up to more current on the neutral conductor than the ampacity of the line conductors. This does not happen on 120/240 systems because like harmonic currents have a 180? phase shift respective of its counterpart.