NEC knows the difference well. Historically the NEC has avoided the term neutral, choosing instead to use the term "grounded conductor" Reason being that not all conductors connected to earth are neutral. Two examples:
1. A corner grounded delta. Here a phase is grounded down. Its far from a center point, but code wants it to be treated like a neutral, ie unfused- and if run through a disconnect or OCPD, it must simultaneously open the hots.
2. A 120 volt only transformer. Technically there is no neutral, just two ends of a single winding. IF feeding outlets or light sockets, code wants one end grounded. Hence grounded conductor- treated and identified like you would with a typical neutral conductor.
Only recently has the NEC decided to use the term neutral, and when it does its only in applications where an actual center point is involved, ie sizing the grounded conductor on a 3 phase or split phase service, not counting the grounded conductor on a MWBC in derating ,ect- stuff that you know only applies to imbalance current.