For a 50 amp, 240 v hot tub, can I downsize the neutral to a #8 ? (#6 Cu phase conductors). Thank you.
It's only money. 30 years ago the difference was maybe only $20.you tell us the cost diff between #6 and #8 for the full installation.
HD #6 THWN 73c/ft
HD #8 THWN 46c/ft
lets say 200ft
#6 $146
#8 $92
diff $54 (retail box store, +tax)
unless you are asking for some pull issue or box or fitting or "have to install 1,000 of these" reasons, i would spend the extra ~$50 for #6.
what say you?
Thank you, actually it was the space, it seems every tub I connect has a 3/4 inch knockout and we use 3/4 conduit. I just thought it might be a little easier pulling, by downsizing. But I haven't looked yet at this tub for manufacture recommendations, I will tomorrow. With the advice so far, it doesn't sound like I will chance downsizing.you tell us the cost diff between #6 and #8 for the full installation.
HD #6 THWN 73c/ft
HD #8 THWN 46c/ft
lets say 200ft
#6 $146
#8 $92
diff $54 (retail box store, +tax)
unless you are asking for some pull issue or box or fitting or "have to install 1,000 of these" reasons, i would spend the extra ~$50 for #6.
what say you?
I see, that's true. A question; I usually use romex 6-3 to the disconnect that has #6 neutral, but # 10 ground. What about the ground size? Thank you.The problem I see is that the code allows dropping the neutral size on a feeder but other than ranges and dryers there is no allowance for downsizing the neutral for branch circuits.
I see, that's true. A question; I usually use romex 6-3 to the disconnect that has #6 neutral, but # 10 ground. What about the ground size? Thank you.
I see, that's true. A question; I usually use romex 6-3 to the disconnect that has #6 neutral, but # 10 ground. What about the ground size? Thank you.
That is not how I see it. 210.19 basically says conductors need to be sized no smaller then the load served, subpart 3 does give a minimum size for ranges and cooking appliances though.The problem I see is that the code allows dropping the neutral size on a feeder but other than ranges and dryers there is no allowance for downsizing the neutral for branch circuits.
yesIs this for a single family dwelling? From your description I assume that it is.
That is not how I see it. 210.19 basically says conductors need to be sized no smaller then the load served, subpart 3 does give a minimum size for ranges and cooking appliances though.
If OP's hot tub requires more then 8 AWG neutral it would be 110.3(B) that would be violated if he didn't comply.
subpart 3 does give a minimum size for ranges and cooking appliances though.
210.19 applies to branch circuit conductors. Is the neutral conductor not a branch circuit conductor? In a two wire circuit both conductors carry same current and will be required to be same ampacity. In a multiwire circuit neutral may never carry same current as the ungrounded conductors in some instances, but they still give a minimum size for for cooking appliances/ranges, I do not see a minimum size for other applications. 210.19(A)(4) does give a minimum size of 14 AWG but that basically means they don't want you to use 18 AWG even thought the load is only 3 amps, and applies to both grounded and ungrounded conductors.Think about it. Those are the hot conductors.. According to your statement then I could run a #14 equipment grounding conductor when the branch circuit is on a 50 amp overcurrent protective device. There are rules for feeders and the neutral being sized not smaller than the equipment grounding conductor but where is that rule for branch circuits?
Exactly the subpart 3 that I mentioned. It only applies to ranges/cooking appliances.Look at exception 2 of 210.19(A)(3)
I am not sure what we are arguing. I did make a typo (thinking one and wrote the other) when I wrote dryers as I really meant cooking appliances.
210.19 says the branch circuits conductors must have the capacity to carry the load however in (3) it gives an exception for the neutral for cooking units... that is the only exception I see.
IMO, and I will leave it at that, the neutral cannot be downsized for a tub, in spite of what the installation instructions state. Would you allow a multiwire branch circuit with a 14 wire on a 20 amp circuit if the neutral would never see more than 15 amps? Maybe you would I just don't read it that way.
You have to deterine maximum load the neutral will see.btw, how would you account for table 310.15(B)(16) for the neutral