In the other scenario you described we would be using the phrase "their relatives are dead".Try telling that to the family of someone that has been electrocuted. Their relative is just as dead either way.
In the other scenario you described we would be using the phrase "their relatives are dead".Try telling that to the family of someone that has been electrocuted. Their relative is just as dead either way.
And these are, in turn, regulated by publicly-controlled bodies. Even the greedy for-profit POCOs have to comply with regulations. They are less prone to fuss about it because they just pass along the cost and say "hey, we have to comply with the safety rules as dictated by the regulators". As long as they make reasonable use of the investments, they are given a reasonable rate of return on their investments.I am willing to guess that the non publicly owned POCO's are the ones that are more likely put off any investigation because of what it may cost in preference of profits.
Please read here:I just want to have a clear conscious and know that I have done every thing I could do to eliminate this neutral to ground voltage.
Thanks guys! The information you shared on stray voltage has helped me to better understand the animal that I am up against. I spoke with the owner of the boat lift yesterday & he says that when he was in the water last weekend he felt the same shock at the aluminum lift beam now as what he felt before the bare bond wire was installed a couple of weeks ago. I havent had a chance to put a meter on it but I know that when I bonded the motor to the water the voltage droped abot 1/2. I bet with the salt water in contact with the wire and corrosion, its back where it was originally. I was wondering about the idea of installing a small transformer to get away from the utility grounded neutral. If I do that I would still have to deal with the EG. Not so sure how thats gonna get rid of the voltage Im seeing coming of the grounded motor frame. I saw where MH appeared to share the same disgust over this problem with swimming pools as I am experiencing with the boat lift located over water.
You can install a code compliant and safe system that will make this problem go away with a creative application of 250.110 as I stated in an earlier post.The fact that the EGC is connected to the utility neutral is the problem. Anything that you add must still have EGC and the problem will not go away. ...
So now when there is a fault on the bolt lift we will energize the metal parts as measured to the water with a fatal amount of voltage as opposed to the few volts it is now energized with!!!...
My opinion until POCO fixes problem is to disconnect the boat hoist including the EGC from the on shore structure it is served from. ...
So now when there is a fault on the bolt lift we will energize the metal parts as measured to the water with a fatal amount of voltage as opposed to the few volts it is now energized with!!!
You can install a code compliant and safe system that will make this problem go away with a creative application of 250.110 as I stated in an earlier post.
In general there will still be an connection to the utility grounded conductor via the primary EGC. This is where you have to use a provision that exists in 250.110....
If you use a GFCI breaker on the circuit that feeds the boat lift, then can you use an isolation transformer and break the EGC conductor between the main panel and the boat lift. In this case the EGC on the secondary of the isolation transformer would be connected to that secondary and a ground rod at the boat lift.
.
110604-0850 EDT
rutsd:
To other readers:
If you use a GFCI breaker on the circuit that feeds the boat lift, then can you use an isolation transformer and break the EGC conductor between the main panel and the boat lift. In this case the EGC on the secondary of the isolation transformer would be connected to that secondary and a ground rod at the boat lift.
gar, I have not personally put my meter on the neighbors lift beam that is connected to the grounded motor but the neighbor told me that he noticed the voltage problem approx. 2 years ago and he decided to bond his lift motor with a piece of copper wire and attach that to a rod which is in the water. He says that the rod is now corroded and is not as effective, He plans to replace the rod and its connection. I will have to ask him when I am there next but he doesnt seem to be concerned with the amount of voltage he is seeing. I will report back with voltage readings.
This problem is the reason the code added the perimeter bonding requirement a few cycles ago. Prior to this the bonding connection energized the water and there was a potential between the unbonded deck and the water....
You do not have this problem with a properly designed swimming pool beacuse unlike a river or lake, the pool has a grounded rebar cage all around it and just about any metallic equipment in or near the pool is also bonded to the same point as the cage.