- Location
- Illinois
- Occupation
- retired electrician
No, there is no requirement to run the grounded or neutral conductor to a panel or equipment that does not need it. There is no violation in running only the 3 phase conductors and an EGC to such equipment. In my example the SDS is a grounded system and feeds both a lighting panel and an MCC. There is no code requirement to run the grounded conductor to the MCC as long as it does not supply any single phase line to neutral loads.With code this would be a violation of 250-20(B)(2), you would need to be 480v delta 3w ungrounded for the MCC and you cannot feed a 277v system as ungrounded so one of these needs to pass through a SDS to enable it.
Like I said much earlier in this thread, it is my opinion that the change in the defintion of grounded makes 250.34(A) void. It is simply not possible to have a grounded system without a grounding electrode because of the change of the definition of grounded.With 250-34(A) "the frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250-52 for a system supplied by the generator", it's simply not required.
As far as the defintion of premises wiring I only mentioned that because many say that a portable generator does not supply premises wiring.
Don