I declare either I am blind or have no reading comprehension at all as I can not see where there is a conflict with 250.20 and 250.34
II. System Grounding
250.20 Alternating-Current Systems to Be Grounded.
Alternating-current systems shall be grounded as provided for in 250.20(A), (B), (C), or (D).
Other systems shall be permitted to be grounded.
If such systems are grounded, they shall comply with the applicable provisions of this article.
250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by the generator under the following conditions:
Where is the conflict?
If there is a conflict could someone please take the time to point it out?
II. System Grounding
250.20 Alternating-Current Systems to Be Grounded.
Alternating-current systems shall be grounded as provided for in 250.20(A), (B), (C), or (D).
Other systems shall be permitted to be grounded.
If such systems are grounded, they shall comply with the applicable provisions of this article.
250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by the generator under the following conditions:
Where is the conflict?
If there is a conflict could someone please take the time to point it out?