ibew501ed
 - danbury ct/work in white plains ny
I think the GEC is the larger black wire w/white stripe between #4 and #5 of post 17....?
Thanks, I didn't see that but 480sparky brings up a good pointibew501ed said:I think the GEC is the larger black wire w/white stripe between #4 and #5 of post 17....?
I usually land the water main ground on the screw lug next to the service neutral typically because it's a larger conductor and in some cases can't fit under the screw terminals of the neutral buss. The supplemental GEC conductor for a residence is never larger than # 6 and can be installed on the buss. Although it's not required I typically run it in green for easy identification. That's just my anal retentive way of doing things.480sparky said:If it's not, and it's the grounding cond. of a 4-wire cable, then the neutral should not be bonded.
Depends on where you are. Some jurisdictions don't allow it claiming that once it's locked inside the meter enclosure it is not serviceable. Personally, I think it's a crock.EBFD6 said:also GEC could be landed in the meter socket.
As I'm sure you know a lot of things come into play when upgrading a service (i.e. space requirements, number of existing circuits, expansion capability, etc.). In the photos it appears as if the installer didn't plan well and made no provisions for expansion but we don't know all the particulars. The more I think about it and from my recollection I don't believe that the Sq D QO panels are mechanically designed to only accept tandem breakers in specific slots although Sq D has made some provisions in the design of their tandems. The QO panel covers usually tell where and if tandem breakers can be installed. Whereas, the Homeline panels will have notches in those spaces that allow tandems, but I don't believe the 150 amp, 30 circuit panels have that feature. BTW, I haven't seen a 30 circuit, Sq-D QO main breaker panel for sale over the counter but I could be mistaken. Is this really a 200 amp service ? I can't see the raised numbers on the main breaker handle.PetrosA said:I don't get the whole idea of using 30 circuit panels in the first place. One tandem is going to push the cost up as much or more than using a 40 circuit panel to begin with. So space would be the ONLY thing that would convince me to use one.
BTW, do the QO panels have specific bus locations for tandems?
I got a dollar that says the pigtail is not in that wirenut, but goes to the top right neutral terminal.
I'm curious as to why GFI breakers.
the left SEC was hot to the touch and the right was normal. Both wires had a 25 amp load on them when read with an amp meter. I advised the client to have the power company check the meter connections as the connections in the panel looked ok.
If it's hot to the touch then there is a bad connection. At 25 Amps there shouldn't be any feeling of heat. Now it may be where the lug connects to the breaker but it's still a bad connection, somewhere close, cable will act as a heat sink. ( something had to produce the heat).
I agree....if this had been a service call I would have cut the seal on the meter and taken a look but since it was a pre-sell inspection on a new home it's best not to make too many waves!
Plus you made a good point...it could be a bad main breaker. I need to get me an infrared camera.
I twist the whites and blacks of such circuits, as well as 2-wire 240v ones, together at rough to minimize that.He probably hasn't use to many arc faults before and hasn't gotten used to keeping those circuits seperate when landing his neutrals.[/left]
I'm no private investigator, I'm not going to zoom and enhance and all that, but it really looks like there is a plastic skin over the aluminum on the left conductor. You sure you got it off?FWIW...the left SEC was hot to the touch and the right was normal.