Depends on the poco too, Georgia Power prohibits it from being in their equipment, while other poco’s want it terminated there.
See, that’s where I disagree.
The Meterbase is owned by the consumer on our system.
The meter is in the customer’s equipment.
 
See, that’s where I disagree.
The Meterbase is owned by the consumer on our system.
The meter is in the customer’s equipment.
With Georgia Power, you can own it, or they can own it. Either way they will not allow the GEC in the meter compartment, or the CT cabinet. I don’t know if they still do, but BRMEMC wants the GEC continuous all the way up the mast on overhead services, and they crimp it with the neutral at the weatherhead.
 
So the GEC is not landed in the meter base? If it were, you wouldn't need the jumpers.
If not landing in the meter socket, CT cabinet, or some other splice box when present in setup like this one I typically would run GEC to one of the panels and a bonding jumper to the other panel. Kind of personally think GEC to one panel is sufficient, particularly if the service conductors are tied together pretty much on opposite side the wall in a meter cabinet, but NEC just not worded to accept that. Bonding jumper does create a place for current to parallel.
 
Am I the only Electrician that installs load centers with the main breaker on THE bottom ? Saves Service cable and gives you more room on the one side of the panel. I do mostly residential work. Just try to get a Arc/GFCI breaker on that side of the panel.
89cff47fc6ae9732bcc7368c94bdcbe8.jpg


Sent from my Pixel 4 XL using Tapatalk
 
Am I the only Electrician that installs load centers with the main breaker on THE bottom ? Saves Service cable and gives you more room on the one side of the panel. I do mostly residential work. Just try to get a Arc/GFCI breaker on that side of the panel.
89cff47fc6ae9732bcc7368c94bdcbe8.jpg


Sent from my Pixel 4 XL using Tapatalk
Some erroneously call that panel "upside down", I maintain that the main lugs/ breaker should be at the end where the conduit/cable enters, there are always exceptions to the rule.
 
Am I the only Electrician that installs load centers with the main breaker on THE bottom ? Saves Service cable and gives you more room on the one side of the panel. I do mostly residential work. Just try to get a Arc/GFCI breaker on that side of the panel.
89cff47fc6ae9732bcc7368c94bdcbe8.jpg


Sent from my Pixel 4 XL using Tapatalk

1) Many services are fed overhead.
2) If the main is vertically mounted, doesn’t the NEC require “On” to be in the up position?
 
Am I the only Electrician that installs load centers with the main breaker on THE bottom ? Saves Service cable and gives you more room on the one side of the panel. I do mostly residential work. Just try to get a Arc/GFCI breaker on that side of the panel.
89cff47fc6ae9732bcc7368c94bdcbe8.jpg


Sent from my Pixel 4 XL using Tapatalk

No inspectors calling you out for not having smokes on AFCI? I’ve always put them on the bedroom lighting circuit so it’s obvious if that circuit has tripped.

I’ve been using the Eaton BR on resi lately because they have that short body PON AF & GF. Square D recently changed their dual-function breakers to have a short body (still slightly longer than regular breaker) but I haven’t seen any available here yet.


Sent from my iPhone using Tapatalk
 
Looks like a handle lock to prevent breaker from being unintentionally turned off.
That style can keep it from unintentionally being turned on or off.

Will still trip if called upon to do so, just need to take the attachment off to reset it.

That however doesn't comply with 110.25 for disconnecting means that are required to be lockable.
 
That style can keep it from unintentionally being turned on or off.

Will still trip if called upon to do so, just need to take the attachment off to reset it.

That however doesn't comply with 110.25 for disconnecting means that are required to be lockable.
True, there is other device for "lockable" for LOTO purposes.
 
No, this County requires 15 amp standard breaker with handle screw device to prevent occupant from turning off. 14/2 to first smoke then 14/3 to interconnect them. They recently added the carbon monoxide requirements to go along with the smoke. I can attach file if you want to see it.

Sent from my Pixel 4 XL using Tapatalk
 
Do they also require battery back up as well?
I can see why they may do it as an amendment.
I take it they will also not allow any other items added to this circuit.

I would like to read it just for my own curiosity.
 
From looking at the pic it looks like receptacles (outlets) are on #12, 20 amp lighting #14, 15 amp.
Is this also part of there rules?
Post up a link to the amendments.
May be some good read.
Thanks
 