kwired
Electron manager
- NE Nebraska
- EC
From Art 100:
Per these definitions the #2 conductors between them and the service disconnecting means are also included.
I don't think it is the intent to size the GEC per the total area of those #2 conductors, and don't see why they should be sized per those conductors.
If one were to put a 150 amp main breaker on the incoming 1/0 (presuming it is copper) and leave everything else the same as far as routing of ungrounded conductors went - now you have essentially the same thing but smaller service entrance conductors and can use a smaller GEC. Makes no sense to me, though I see how some how some are interpreting it.
Too much emphasis is put on grounding electrodes, that short amount of #2 already inside the building isn't going to have that much impact on how much of a surge might enter the building from lightning or if a high voltage line fell onto a low voltage line. That is mostly dependent on the incoming 1/0.
I am not interested in trying to submit any changes to this so don't tell me to do that either. It is what it is for me, and I will deal with it if ever questioned on such a thing by an inspector. If no building steel or metal water pipe - usually only concerned with having #4 to the CEE and/or #6 to any rods anyway.
The incoming 1/0 conductors are service entrance conductors.Service-Entrance Conductors, Overhead System.
The service conductors between the terminals of the service equipment and a point usually outside the building, clear of building walls, where joined by tap or splice to the service drop or overhead service conductors.
Service-Entrance Conductors, Underground System.
The service conductors between the terminals of the service equipment and the point of connection to the service lateral or underground service conductors.
Informational Note: Where service equipment is located outside the building walls, there may be no service-entrance conductors or they may be entirely outside the building.